Comparative difference between 33Kv & 66KV for transmitting
the load of 7 MW at a distance of 34 Km.
Answers were Sorted based on User's Feedback
Answer / kapil
transmitting through 66kv is better than 33kv because losses
in 66kv is less as compare to 33kv line.
| Is This Answer Correct ? | 46 Yes | 7 No |
Answer / bharat kanojia
As losses are inversly proportional to square of 'v'.
therefore 66kv could be a better option, but as the line is
a short transmission line,cost factor would come into
picture,hence accomodating everything 33kv is the most
fitting.
| Is This Answer Correct ? | 24 Yes | 5 No |
Answer / ayush
1.as voltage of line is increased current is decreased.so
the copper losses associated wth current r reduced.but iron
losses dependent on voltage r increased.as the supply
voltage is constant so r the iron losses.but copper losses
vary wth load(load current)bcz current is less we cn say
that overall losses i.e. cu nd iron losses r reduced.
2.as nw supply votlage is increased size of current
carrying conductor reduces as current is low so less area
required for power dissipation.
3.as losses r less so higher is the effiency of line so is
the power transmission capability.
| Is This Answer Correct ? | 12 Yes | 0 No |
Answer / shafiq
if there is short trasmission line it has negligible
inductive losses. there4 v prefer 33kv trasmission for this
load & order to save capital cost of the system.
| Is This Answer Correct ? | 5 Yes | 2 No |
Answer / ganesh9703840484
7mw load is huge load.to travel 34km it is come under
medium transmisson line.so it is necessary to reduce the
losses. if the voltage is high current becomes less.so
copper losses are reduced.so 66kv transmission is preffered.
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / r k gupta
You have to find break-even cost for capital expenditure and running expenditure for both 33 and 66 kv system. Optimise the load at which 66 kv system survives the capital cost. It's simple
| Is This Answer Correct ? | 0 Yes | 0 No |
Why the underground cables will Punchar? or what is the reason to burst the underground cables?
why two wires are wound alternately to each other in single phase wires?
how to calculate the chiller load from TR to KW?
why not starting switch first connect in direct on line starter?????
how to calculate the watts from the tr
Has someone here done a sizing for a generator (3 phase), its for a pumping station. If you have an example for standby/duty and both running (I) star delta (ii) Soft Starter.
Why cant we connect the motor output to generator and then generator output to motor ?
If 11 KV breaker on the primary side of a 11 KV/3.3 KV 12.5 MVA transformer can be installed at a distance of 1000 mtrs through a 11 KV cable. If no what are the probable reasons.
The transformer which is smallest in size is and how to calculate that? The options are 100 KVA, 50 Hz 100 KVa, 100 Hz 100 KVA, 25 Hz 50KVA, 25 HZ
4 Answers Ranbaxy, Zee Laboratories,
What are the advantages of individual drives?
1 Answers A1 Electricals, Suzlon,
Three phase star connected PT transformer primary side one phase fuse is blown what will be the output in secondary side(Secondary side also three phase star connected)
How to get a multiplier in 11kv energy meter?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)