how can alculate the apfc panel rating?
Answers were Sorted based on User's Feedback
it depends on type of load ,calculate avg power factor of
load than consider p.f. of transformer than you can get
value of apfc rating
| Is This Answer Correct ? | 16 Yes | 1 No |
Answer / karanth.sp
The PF of the connected load to a particular transformer is
to be asssuemed or known exactly.If the transformer is
already loaded you can kow the running PF by PF meter
connected.IF the PF is say 0.7 & you want to improve to
unity.You must add a capacitor of Total load in KW multiply
by a factor of 1.02.That is the value of Capacitor in KVAR.
Formula is PF (cos0)=0.7 Tan01=0.963
improve PF(Cos0)=1 Tan02=0
KVAR Required= P(Tan01-Tan02)=P(0.963).
This shall be devided in to number of stages as required.
| Is This Answer Correct ? | 9 Yes | 5 No |
DIFFERENCE BETWEEN NORMAL TRAFO AND THRISTER TRAFO?
What is 2P*0.5 sqmm screened copper cable and what is the use of it..?
The sodium vapor lamp is not glows when it is connected a distance of 5 meters above from gearbox, why ?
why DG neutral is earth?
what is meant by neutral Ct of a transformer and how it connected in transformer
We have one Energy meter for Measuring the voltage,current,power,energy(KWH,KVARH,KVAH) & power factor.The problem is that the meter does not show whether the PF is lagging or leading.So i want to know that is there any way or calculation to find out that whether the PF sign (lagging or leading) depending upon the above mentioned parameters?
Why we Do not connect the windings of the motor in delta? & what would happen if we do that? I mean the winding themselves not the three lines that are coming to the motor?
what are the types of electromagnetic forces developed in practical transformer?
0 Answers APC, BPCL Bharat Petroleum, Electrical Tech,
How i can identify the 220V and 110V power supply equipment? No tag number.
Why don't connect earth wire to elcb?if earth fault occur,how will detect it
1 Answers TATA, Tata Communications, Telecommunications,
When we are working on transformer(132\11KV). we are going to isolate the transformer from both HV side and LV side. then we are applying grounding on both side. My question is that we required to isolate the VT which is still connected from secondary side.?
i m doing DEEE in part time,can i join regular cources in BE,,IF i join what the cources can i select like (civil,ece,IT) ,,kindly advice
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)