WHAT ARE THE DATAS REQUIRED FOR SCS SIGNAL LIST PREPARATION?
It depends on your SUB STATION CONTROL SYSTEM (SCS)
supplier and client, and load despatching authority SCADA
system.
Generally Load despatching authority demand:
I) Remote control -on-off control oF CB,STATUS OF
INDICATION,PROTECTION AL+TRIP SIGNALS ,FEED BACK SIGNAL.
OLTC COUNTER,
2) INDICATION - A,V,F,PF, MW,MVAR,
3) METERING IN -OUT MWH,MVARH,
4) sTATUS OF ALL CB,DS,ES, PLC,
5) MAIN BUS ,INCOMMING,OUT GOING.
6)SUB STATION dc VOLTAGE, UPS ALARM
7)FAULT LOGGER REPEATITION SIGNAL.
THIS IS A VERY EXPENSIVE TASK. SCS SUPPLIER MUST FINALIZE
CLEARLY,AFTER FINALIZING SIGNAL SUCH ,AS DI,DO,AI,AO ,LOGIC
SEQUENCES, SHALL PROCEED HIS WORK.
tARIFF METERS ARE VERY EXPENSIVE. SCS MUST FOLLOW LOAD
DESPATCHING REGULATION AND ITS SPECIFICATION.
Is This Answer Correct ? | 1 Yes | 0 No |
Define peak overshoot.
what is the role of reactive powerin transmission and distribution?
Does the isolator has a making capacity????????
What is the purpose of shunt trip in ACB function?
how to select electrical equipment such as fuse,dg,transformer,motor,msb,wire,cable as per the connecting load..please mention any books to design,take licence
0 Answers Gujarat Electricity Board,
Why Nutral CT rating for Earth Fault Protection of Transformer neutral shall be 20% of Full load Current of Transformer
generally rectifying of ac tells. ac signel appear at phase and neutral with respect to frequency by -veand +cycles. but we doesn't experience shock with neutral in house hold ac??????.
11kv = LT 440v , how many amp.supose 440v side 5000 amp curent drown
In power transmission using open belts or horizontal shafts it is preferable to have the slack side of the belt on the top because
What is the minimum insulation value required for a cable between phase to phase and phase to earth of 380 Vac 50Hz circuit, having load arround 800 amps.
why do motors burn out? I understand why adding parallel loads to a power source means more current moves through the circuit, and can destroy circuit elements by overheating. What about when you have a vaccuum cleaner intake flush against a floor, a room fan sitting directly against a wall, or a power drill trying to drill through something too hard?
Why reverse power relay is used?