how to size a diesel generator set?
Answer / mahesh sali
mostly total electrical cal.in KW at 0.8 pf as per thumb
rule.
KVA = KW/PF
as per nec code norms ur dg set shall be suitable to take
the higher inrush current during starting.
so awalys keep some say 115% to 125 % on induction motor
load.
for ups & lighting system around 200 to 300 %
Toatl kw rating = 1.25 * Kw ( Plant load )
KVA at 0.8 pf = Total kw/0.8
Assume that Dg set loading at 70%
i.e rated KVA = KVA /0.7
adding some 20% future load
i.e. actual DG ser rating in KVA = rated KVA + rated KVA *
20%
Thanks
| Is This Answer Correct ? | 1 Yes | 0 No |
why use delta star x-mer in distribution system.
WHAT IS REACTIVE POWER?
how to erect roof control panel?
what are the different pre- commissioning tests performed on distribution transformer, power cable and switchgear?????
What is the meaning of Dyn11 of Transformer.
A 4-Pole D.C. Generator has a speed of 1500r.p.m. Then what will be the frequency of D.C. Generator ?
Explain what are inter-poles and why they are required in a dc machine.
what is a relay?
Write a note on RC operational amplifier as integrator
why ht motors are star connected?
The earth pin of some three pin plugs are seen split. why?
what happens if we connect two parallel ideal voltage sources across resistor?what is current flowing through resistor?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)