Answer / mahesh sali
mostly total electrical cal.in KW at 0.8 pf as per thumb
rule.
KVA = KW/PF
as per nec code norms ur dg set shall be suitable to take
the higher inrush current during starting.
so awalys keep some say 115% to 125 % on induction motor
load.
for ups & lighting system around 200 to 300 %
Toatl kw rating = 1.25 * Kw ( Plant load )
KVA at 0.8 pf = Total kw/0.8
Assume that Dg set loading at 70%
i.e rated KVA = KVA /0.7
adding some 20% future load
i.e. actual DG ser rating in KVA = rated KVA + rated KVA *
20%
Thanks
| Is This Answer Correct ? | 1 Yes | 0 No |
what s the differenc between electrical &electronis , how to define them
Explain what is clipper and clamper circuits?
If the ceiling fan is on slow speed, does it consume less electricity?
what is load flow?
Why are cables rated for 40 KA for 0.25 Sec fault current rating?
WHY BLADE & JOW OF ISOLETOR IN SUBSTATION?
what are corona losses
how technical is calculated in 11kv line and lt line
what is the function of 1 phase preventer?
7. A resistance of 30 ohm is connected across 240v supply. If a resistance R ohm is connected in parallel with 30ohm resistor across the same supply, the current drawn becomes triple of original one The unknown resistor R is
What is R/X ratio? I have heard that this ratio is higher in a radial distribution system.Why is it so? I would appreciate a word. Thank you
1 Answers Power Grid, Vignan University,
what is d check in dg 1500kva
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)