Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


how to size a diesel generator set?



how to size a diesel generator set?..

Answer / mahesh sali

mostly total electrical cal.in KW at 0.8 pf as per thumb
rule.

KVA = KW/PF
as per nec code norms ur dg set shall be suitable to take
the higher inrush current during starting.
so awalys keep some say 115% to 125 % on induction motor
load.
for ups & lighting system around 200 to 300 %
Toatl kw rating = 1.25 * Kw ( Plant load )
KVA at 0.8 pf = Total kw/0.8

Assume that Dg set loading at 70%
i.e rated KVA = KVA /0.7
adding some 20% future load
i.e. actual DG ser rating in KVA = rated KVA + rated KVA *
20%

Thanks


Is This Answer Correct ?    1 Yes 0 No

Post New Answer

More Electrical Engineering Interview Questions

what s the differenc between electrical &electronis , how to define them

9 Answers  


Explain what is clipper and clamper circuits?

0 Answers  


If the ceiling fan is on slow speed, does it consume less electricity?

2 Answers  


what is load flow?

2 Answers  


Why are cables rated for 40 KA for 0.25 Sec fault current rating?

0 Answers  


WHY BLADE & JOW OF ISOLETOR IN SUBSTATION?

1 Answers   BRG, Voltech,


what are corona losses

3 Answers   Siemens,


how technical is calculated in 11kv line and lt line

0 Answers  


what is the function of 1 phase preventer?

3 Answers   ABB, Electrical,


7. A resistance of 30 ohm is connected across 240v supply. If a resistance R ohm is connected in parallel with 30ohm resistor across the same supply, the current drawn becomes triple of original one The unknown resistor R is

2 Answers  


What is R/X ratio? I have heard that this ratio is higher in a radial distribution system.Why is it so? I would appreciate a word. Thank you

1 Answers   Power Grid, Vignan University,


what is d check in dg 1500kva

0 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4453)
  • Electrical Engineering Interview Questions Electrical Engineering (16638)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)