How to convert farad to kvar.
both are the unit of capacitor.
Answers were Sorted based on User's Feedback
Answer / jack
a var is a unit of reactive power
a farad is a unit of electric capacitance
see convert-units.net
Is This Answer Correct ? | 60 Yes | 23 No |
Answer / mgr
Var=VVWC
Where V=Supply voltage
W=2*3.14*F
F=frequency
C=micro farad.
Is This Answer Correct ? | 56 Yes | 19 No |
Answer / dan
var = reactive power, microfarad = capacitance
var = reactive current x voltage = (V/Xc) x V
var = V² x 2ЛfC
Where f = frequency (Hz)
C = Capacitance (μF)
Xc = capacitive reactance = 1/(2ЛfC)
Is This Answer Correct ? | 20 Yes | 2 No |
Answer / cyclone1537
VARs = V²/ Xc = 2*phi*f*C
VARs =voltampere reactive
V =system voltage
Xc =capactive reactance
phi =3.1416
f =system frequency. hertz
C = capacitance, farad
Is This Answer Correct ? | 33 Yes | 16 No |
What is the basic principal of Diesel genarator?
3 Answers Juniper Networks, MRF,
HOW DG WORKS ?
State and define norton’s theorem?
PRV (Pressure relief valve) Trip with oil splash outside power transformers
How does a tertiary winding filter harmonic(espcially 3rd one) from entering into load system?
Why earthing done?
is this the formula of building wiring to get the main breaker.Watts/volts*.8%+higher motor*(25%)=ampere. yes or no or send the correct formula for building wiring.
why we are used D.c. voltage in L.T.side or controling side.we can use UPS also ,in place d.c. voltage
why Y CONNECTION IS BETTER INTERMS OF EFFICIENCY AND P.F FOR A LAOD LESS THAN 40% AND WHY AFTER DELTA IS BETTER FOR > 40%
why eee branch?
if d gen is 50kw,load is 60 kw,hw d gen ll supply d remaining power?
How much CTs are required to measure th curent in DOL starting of motor?PLs explain.