Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


Can any body tell me about Hi-pot test, and why it is
necessary and its procedure of testing

Answers were Sorted based on User's Feedback



Can any body tell me about Hi-pot test, and why it is necessary and its procedure of testing..

Answer / rakesh thakur

HI-pot test is use to test the insulation breakage of
various electrical auxilaries like cables,switchgears
etc.A HI-POT is a autotransformer which produces high
voltage of the desired level of testing, like for 33kv
system we will increase the output voltage of HI-POT slowly-
2 from o to 33 kv and apply it across the testing specimen.
If insulation of the specimen is all right than there will
be zero lekage current(meter affixed on HI-POT) and if
there is any insulation breakage in the system than there
will be certain value of leakage current on certain value
of value of voltage and circuit will got tripped.

Is This Answer Correct ?    5 Yes 2 No

Can any body tell me about Hi-pot test, and why it is necessary and its procedure of testing..

Answer / asif

Dear tech,

because of this test you can know well of your equipment
insulation strength and conductor strength.

Is This Answer Correct ?    3 Yes 0 No

Can any body tell me about Hi-pot test, and why it is necessary and its procedure of testing..

Answer / kanagasabai

HI-pot is High pontential test(or) High voltage test.

Many people are familiar with a continuity test. A
continuity test checks for "good connections." You do a
continuity test by seeing if current will flow from one
point to another point. If current flows easily enough then
the points are connected. Many people aren't familiar with
a hipot test. "Hipot" is short for high potential (high
voltage). A hipot test checks for "good isolation." You do
a hipot test by making sure no current will flow from one
point to another point. In some ways a hipot test is the
opposite of a continuity test.

Continuity Test: "Make sure current flows easily from one
point to another point."

Hipot Test: "Make sure current won't flow from one point to
another point (and turn up the voltage really high just
make sure no current will flow)."

In the simple case a hipot test takes two conductors that
should be isolated and applies a very high voltage between
the conductors. The current that flows is watched
carefully. Ideally not much current will flow. If too much
current flows the points are not well isolated and they
should fail the test.

Is This Answer Correct ?    3 Yes 0 No

Can any body tell me about Hi-pot test, and why it is necessary and its procedure of testing..

Answer / karthik

Hi-Pot test (High Potential) test is used to find out the
insulation strength of a conductor.Usually a voltage of 125%
of rated voltage is applied during the initial test of the
insulation.For any future tests(which should not be carried
out)the applied voltage is less than 100% for not degrading
the insulation.

Is This Answer Correct ?    2 Yes 0 No

Can any body tell me about Hi-pot test, and why it is necessary and its procedure of testing..

Answer / sheik

this test you can know well of your equipment
insulation strength and conductor strength

Is This Answer Correct ?    0 Yes 0 No

Can any body tell me about Hi-pot test, and why it is necessary and its procedure of testing..

Answer / aeccsrpudur

sir
its a high potential test
normally this test is conducted for cables and generator windings
for example if the cable is rated for 11kv and it should with stand 1.25 times of rated voltage during surge conditions
procedure for test - apply dc high voltage 1.25 times gradually and noted the leakage current ,it should be below 100 micro amps for healthy cable for 1 minute

Is This Answer Correct ?    0 Yes 0 No

Post New Answer

More Electrical Engineering Interview Questions

What is single break or Double break related to MCB?

2 Answers  


which type your UPS on line,off line give the reason?

2 Answers   Roto Power,


what is the difference between electrical & electronics

245 Answers   Axon Constructions, Banking, GDA Technologies, Infosys, MBA, Satyam, Satyam Tech, Snow White, TCS,


what is a universal motor? how it works?

4 Answers  


how to find value of resistance when 1 kw consumption for 10 minutes

1 Answers   Manipal Hospital,


state the working principle of incondenscent tube?

0 Answers  


What is the meaning of insulation leavel LI 75 AC 28 About scott transformer spcification

1 Answers  


which will glow brighter?bulb 1 (110v,100w) and bulb 2 (230v.200w) series connection

6 Answers   EnPower India,


Draw the DOL starter and star delta starter drawing?

0 Answers   Danfoss,


What is the difference IN MCCB's between thermal magnetic and electronic tripping system ?

0 Answers  


which of the folowing has negative temperature coefficient of resistance? a. mercury b. copper c. lead d. carbon

2 Answers  


On monitor it is written that current rating is 2.2 Amps. Is it a monitor current drawing capacity or CPU & monitor. If it is only monitor rating, what will be the rating of only CPU and what will be the power consumption rating of PC, Monitor & Scanner? In net, I learnt that computer consumes only 200-300W while running. With the current rating of 2.2 Amps, how it could be 200-300Watts. Please explain?

3 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)