what is mean of 3 by 2 automation ?
Answers were Sorted based on User's Feedback
Answer / farooq
if three sensors installed to measure or monitor one process
variable and when two of them give a high or equal to a set
value than an alarm or correcting action can be activated is
called 2 out of 3 automtion.
| Is This Answer Correct ? | 10 Yes | 1 No |
Answer / senthil
for example,consider the three transmitters are in
service.in logic,the three xtr compare each other value i.e
A&B,B&C,C&A. check the diff of deviation b/w the
comparison.the xtrs showing minimum deviation is taken,from
this the mean is taken b/w two xtrs.this is 2 0f 3.
| Is This Answer Correct ? | 4 Yes | 3 No |
Answer / ladla
this information is apply for alarm and trip system where
these shows the redundant of the system
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / senthil
2 out of 3:
for example:
we use three pressure transmitters in the process line
discharge of a pump.consider the range is ( 0 to 10 bar).we
have a condition that when the discharge pressure is low the
pump has to trip(less than 4bar).
-if two transmitters goes below this value there is trip.
we have deviation alarm,deviation deadband warning also in 2
voting 3 concept.
| Is This Answer Correct ? | 1 Yes | 1 No |
Answer / gopi
step by step implimentation our logics by using any controller
| Is This Answer Correct ? | 0 Yes | 1 No |
Dear friends, I have a question: We work on a project which has some boilers to provide steam for desalination unit. The boiler area is safe and the only hazard source is the fuel lines of boilers. I want to know according to NFPA standard which type of instrument should be selected on the fuel line: Eex Type or Non-Eex type? Thanks in advance
how to replace the smart transmitter software
what is the deferance between LCN and UCN.
what is Potential free contact? where it is used?
3 Answers Engineers India Limited,
What should be the stanchan Height for installation of Smoke detector & toxic gas detector in field,according to qatar standard
What is the load line in control valve?
which processor is used in dcs.
0 Answers ABB, Wave Distillery,
How is PH sensor works ?
how the arrangement of equipments done in control room
hw to calibration a control valve?
Explain an adaptive / self-tuning controller’s major draw card.
why 4 to 20 ma used at 0 set
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)