Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


hw to calibration a control valve?

Answers were Sorted based on User's Feedback



hw to calibration a control valve?..

Answer / aftab ahmed mazari

Following procedure should be done for control valve
calibration.
Suppose it is spring loaded and direct action.(Direct
action means at top of diapgargm signal and with the
increase of signal, stem will move downwards or the stem
will extend).Also valve is signal to close. Check its Bench
Set. Suppose it is 6 to 21 PSI.
1. Set pressure regulator of positioner at about 30 PSI.
2. Apply 3 PSI (4 mA if positioner is smart or electronics)
signal to Positioner.Gradullay increase signal. Note the
movement of stem.
3. Apply 6 (8 mA),9 PSI (12 mA), 12 PSI (16 mA) and 15 PSI
(20 mA) signal. Valve stem should move accordingly and
indicator must show 25%,50%,75% and 100%.
4. If error, remove it from zero and span of positioner.
5. If facing any error problem, give signal 50% and then
remove error. Rest will be ok automatically.
6. Suppose valve is normally closed and at any vent service
and signal to close as I mentioned earlier, then make shut
close of valve at 14.5, or 14.7 PSI. Valve may start
closing at 2.75PSI.
7. If valve is at control operation, like level, pressure
etc, then calibrate it accurately.No need to calibrate it
at 2.75 and 14.5 PSI.
aftabmazari@yahoo.com

Is This Answer Correct ?    31 Yes 3 No

hw to calibration a control valve?..

Answer / r.murugan

IF ITS PNEUMATIC CONTROL VALVE FIRST WE HAVE TO CHECK
INSTRUMENT AIR PRESSURE THEN WE HAVE TO REGULATE THE
INSTRUMENT AIR PRESSURE REGULATOR TO I/P COVERTER AND
PNEUMATIC POSITIONER
BEFORE STROKING THE VALVE WE HAVE TO CHECK VALVE AT NEUTRAL
POSITION IF NEUTRAL POSITION THEN ONLY CAN MOVE THE THE
VALVE
IF AIR TO OPEN VALVE WHEN COMMAND 4ma VALVE POSITION SHOULD
BE CLOSE (DIRECT OPERATION) LOCAL WE HAVE TO MECHANICAL
SCALE CLOSE INDICATION
THEN INCREASE THE CURRENT 4.5ma TO 5ma to check the start
of opening the control valve
then gradually can increase and decrese the current and
corrospondingly check the stroke momemnt based on command
we have to check the feedback

Is This Answer Correct ?    16 Yes 7 No

hw to calibration a control valve?..

Answer / sajid ali khan

In addition to the Calibration, it is also crucial that the
Control Valve (CV) response matches the demands of the
controller.
Normally, the CV is calibrated and checked as already
mentioned in this post, but please appreciate that in real
operation, for most of the time the controller output will
change in very minor amount to counteract the process
upsets or set point changes and the CV need to respond
rapidly and effectively to those changes. Thus if you
observe any CV, or note its trend from the Control System,
you will see movements in fractions of mA/psi etc. Very few
CVs will go to the full close position and valve going to
the full open position is even rarer.
Also, it is necessary that the CV overcomes any stiction,
has minimum hysteresis as well as little dead band.
Therefore, it is important the valve be checked for minor
changes.
How to check that:
1. Move the valve to any position other than at its
extremes, somewhere in the middle.
2. Find a safe spot on the CV stem where you can feel the
minor CV movement against a fixed part of the CV Body. Put
your finger firmly on that spot of the CV Stem. I
repeat “SAFE SPOT,” otherwise if the CV operates suddenly
your finger may be injured.
3. If the CV has a digital positioned with a feedback, the
observation may be simpler and finger feeling may even be
not necessary at all.
4. Now closely observe the CV input signal, preferably the
pneumatic signal on a 6 inch dia pressure gauge of at least
0.5 % accuracy. If digital pressure indicator of similar or
better accuracy is used that would be better.
5. While applying input signal move the CV a small amount,
then apply reverse signal very gently and slowly, and feel
the CV stem movement with your finger, the stem should
move. The numerical value of the input signal against the
minor can be noted from the factory test data of the valve.
In case that is not available it would be known by
experience.
6. Repeat this exercise at two or different CV openings and
always check in forward and reverse directions, till you
are confident of the CV performance.
7. In case valve sticks, shows excessive dead band etc,
then loosening of the stem packing or even CV opening for
inspection to check stem/plug misalignment, or hardened
stem packing may be the culprit.
Regards,
Sajid Ali Khan
engineersajid52@gmail.com

Is This Answer Correct ?    7 Yes 5 No

Post New Answer

More Instrumentation Interview Questions

what is the difference between E/P positioner and I/P positioner in control valve , in which application the respective positioner are used in.

1 Answers   ABB,


How can I map a tank?  Tank 15m h and 42m dia. we just fixed radar type lit. its reading shows over range. Now its required mapping ?

1 Answers   CMC,


what is the difference between SMART and tipical transmeter ?

3 Answers   Sirte Oil Company,


what is the vital subject for scoring bhel exam&what is the question pattern

0 Answers   Bhel,


can i use capillary type dp transmitter converted to capillary type pressure transmitter. if i removed one side capillary tube its work correctly?

1 Answers  


Can be operate control valve without positioning if yes ? how and why?

4 Answers   Focus,


I am teja. I am studying Msc(tech) Electronics and Instrumentation (3years course) in Andhra university. But my course is not recognised by UGC and AICTE. Please tell me the job opportunities after this course. And i fineshed PLC course in IGIAT ,Vizag.Also complted my short term coure in SCADA, Seimans WinCC in ATI,Hyd.After Msc can i join Mtech for good job? or phd. How i can get good job in INdustrial Automation Side. Please give replay.Because this is my life matter.

0 Answers  


Control valve question what is the meaning of cauge.?what is the use of cauge?

1 Answers  


deference between DCS and PLC including date processing and architacture.

11 Answers   Jindal, Shell,


What is full form of hart communicator?

2 Answers   KOC, UPL,


Yokogawa CENTUMVP R6.09 unable to download to Engineering Station with ExaOPC R3.75 The issue is when I try to download the common project section to the Engineering Station (STN) from the HIS in System View, it is unable to connect. The error displayed is: WARNING: Could not connect to equalize destination. (7001) Retrying. Number of retries = 0/1 ERROR: LdXopsLoadMain: connect error 10060 ERROR: Processing terminated due to connection error. (7002) Equalization end with errors. STN0149 ---- ERROR = 2 WARNING = 1 ---- Background: >Updated the ExaOPC software on the STN from 3.60 to 3.75 >STN operating system is Windows Server 2008 R2 >HIS operating system is Windows Server 2016 Stanard Solutions attempted include: >Ensuring all IP addresses are correct and all networked devices can be pinged. >The ability to ping a device using its host name from another device (<ping STN0149> from HIS) >Ensure both devices firewalls are disabled. >The antivirus installed on the STN is disabled. >Ensuring both devices are within the same workgroup. >Added both devices to each other's Host and LMHost files. >Running IT Security tool after changing any administrative settings.

0 Answers  


what is isloted barrier how it works and what are the main purpose.how it make safe area.

0 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4453)
  • Electrical Engineering Interview Questions Electrical Engineering (16638)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)