How to calculate the size of the cable? for exp i want to
use the load of 10HP
Answers were Sorted based on User's Feedback
Hai
its is very simple
load=10 HP
10 X 0.746= 7.46 KW
7.46 X 1000/ ROOT 3 X 0.8X 415= 12.97 A= 13 A
So our require cable shouls be withstand 13 A AT full load
condition .
u will reff any one cable manufacture catalouge which
cable suitable for the same load . but that cable to be
suitable for Appx -18A because u will consider the
derating factor for cable .
| Is This Answer Correct ? | 6 Yes | 1 No |
Answer / santosh
Sqmm of cable depends upon the cable material.In thumb rule Cu cable can carry 10-12 times of its rated sqmm.For ex 10 sqmm cu cable carry 100-120 amps.Al cable carry 4 times current of its rated sqmm
For ur problem: 13A is rated current. 50-60 amp staring current,7-8 running cu.So u may need 4 sqmm Al cable or 2.5 sqmm cu cable.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / charan
fine buddy, what i want is how the manufactures is deciding
that Sqmm of the cable ??
| Is This Answer Correct ? | 0 Yes | 6 No |
How to find the maximum load(in KW)in a big industry, having motors,lights,lifts etc..?
what types of load we get from the national grid? is this capacitive or inductive?
what is O.T?specify the acceptable range?
why transformer is rated in kva?
why motor starting current is High ?
any body,pls tell me how to done relay coordination ? how to coordinate by TCC curve?how to read the tcc curve?
what is threshold voltage for a relay???what does it exactly means ?whats its value in our indian transmission system say 11kv feeder RMU relay
At 765Kv, I have seen the use of PT at line side for metering and CVT for protection, although as far as my knowledge is concern, PT at this voltage level will have huge loss and more cost as compared to CVT as CVT can also perform same function of Protection and Metering? So my question is why use PT and not CVT for metering and protection in order to reduce the cost.
Why we are always only used 11 kv. , 22 kv ,33kv in transmission line? Why not use 25, 55 ,65 kv ?
3 Answers Khidmah LLC, Precision Camshafts Limited,
how can calculate resistance box for 15 kw, 6 pole, RV-230, RA-42 motor
Why it is necessary to isolate fire fighting when you are taking shutdown for lv board.
Why is it that North America uses 60 hz frequency while Europe uses 50 hz?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)