keeping in view of parallel operation which of the 3 phase
transformer connection are possible?
a)delta-delta to delta-star b) delta-delta to star-delta c)
star-star to delta-delta d) delta-star to star-delta
Answers were Sorted based on User's Feedback
Answer / nadeem
B.delta-delta to star-delta not possible parallel
operation.
C.star-star to delta-delta that is possible parallel
operation.
D.delta-star to star-delta also that is possible parallel
operation.
A.delta-delta to delta-star not possible parallel operation
but im not conferm.
| Is This Answer Correct ? | 50 Yes | 10 No |
For parallel operation of transformers as you know the
requirements, 1. magnitude of the voltage, 2. phase angle
difference between the i/p and o/p voltages, 3. equal
percentage impedance of the transformers.
I don't think that whatever you are asked configurations
same vector symbol will get. So we can't do paralleling.
if you get the same phase angle difference ypu can go ahead
with paralleling.
| Is This Answer Correct ? | 16 Yes | 10 No |
Answer / vikas tomar
If the transformers are star-star or delta-delta, they can
not be paralleled with star-delta or delta-star,As there
will be the phase difference of 30 degree b/w the secondary
voltages for the same supply voltages across the primaries
of the two transformers.It will result the circulating
current in transformer windings.
Hence option (d)is correct answer.
| Is This Answer Correct ? | 6 Yes | 0 No |
why do harmonics generata?
Dear Friends, I have a 500KVA transformer supplying whole factory having 3 phase and single phase mixed loads. Power room has ammeters connected via CTs for individual phase. Now I know that readings shown on meter for each phase say R,Y and B are line currents. But when I want to know the total on transformer do I need to add the currents of all three phases readings shown on meter or value for anyone phase will give me the correct power load on transformer for that point of time. 2. If ammeter shows unbalanced readings for R,Y, B phases say 150, 250 and 300 respectively so can I assume that 150A i.e average of 3 will be the 3phase load currents and remaining will be 1phase currents. Please clarify my doubt.
Don't you have similar question banks related to Oral Certification Examination conducted by Mercantile Marine Departments / Directorate of Shipping, Ministry of Shipping for Electro Technical Officer?
0 Answers Bernhard Schulte Shipmanagement,
Going in for a three phase motor or a single phase motor, what factor should be considered for this? For eg., to pump water to certain height and such domestic applications, which motor is suitable?
what is auto re-closer?
what is max. continous current of LT side of distribtion transformers? ie for25kVA, 63kVA, 100kVA, 200kVA etc
why aggregate is placed all around substation ground.
HOW TO CALCULATE THE CAPACITOR RANGE FOR LOAD FOR PF IMPROVEMENT? EXPLE:FOR 65 HP LOAD HOW TO CALCULATE CAPACITOR RANGE?
12 Answers Al-Malik, All Star Electric, GEC, Reliance, Universal Industries,
what is the difference between ac ground and dc ground.. In my project iam using both ac and dc supply.. can both the grounds or the return paths be connected??
which type of motor complete it's one rotation in 30 day's.
why only 11kv level is used for transmission purpose? why not 230v?
what is sevice settings for mccb?How can be it setted?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)