Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


why DG rating in kva

Answers were Sorted based on User's Feedback



why DG rating in kva ..

Answer / zulfiquar

All the machines we are using like transformer, DG's are
all in KVA becoze at that particular time we dont know the
consumer power factor as we know (Active power= apparent
power x power factor) KW= KVA x Cos phi, that is why we
have machine in KVA rather the KW

Is This Answer Correct ?    22 Yes 1 No

why DG rating in kva ..

Answer / jagjeet

Because DG set acting as a power source and supplying
to differnts loads .

Is This Answer Correct ?    8 Yes 6 No

why DG rating in kva ..

Answer / subodh kumar

becouse alternatar have two type losses
1. iron losses
2. copper losses
so we find the iron losses in voltage & copper losses find
in amp that is why we take reating in KVA

Is This Answer Correct ?    2 Yes 1 No

why DG rating in kva ..

Answer / tarkeshwar

As we know D.G. set i used to generate the Power . it
generate Active power & reactive power(Apperentus
Power=Active Power P+ j Reactive Power Q) and we consume
only active power(KW) that's why the DG rating is in KVA or
MVA, these are the unit of Aperantus Power

Is This Answer Correct ?    4 Yes 6 No

why DG rating in kva ..

Answer / g c a

IN DG's load is decided by the users.... wheather it is
inuctive load or capacitve load......... so that's why
it's in KVA

Is This Answer Correct ?    3 Yes 8 No

why DG rating in kva ..

Answer / stanley

In DG, the armature has conductor loss (Ia). it give output
voltage with conductor loss. Tth electrical loss is in Amps
(I). So kilo volt +Ampere=KVA

Is This Answer Correct ?    3 Yes 8 No

Post New Answer

More Electrical Engineering Interview Questions

For high voltage and low current Circuit Breaker preferred is vacuum circuit breaker.why?

1 Answers  


why the desirable efficiency for a motor is 60%, but in case of transformer, it is above 90%?

1 Answers  


which tap of the transormer you will use in critical condition(worst)?

1 Answers  


what is the working process of over & under voltage relay.

0 Answers   NTPC,


What should be the earth pit resistance value?

7 Answers   BARC,


in case of OC+EF relay, how the burden is divided/calculated/shared by the CTs in case of normal (healthy condition) and during fault conditions.? three coils of OC & ef coil is conected in residual connection across the three CTS.

1 Answers  


What meant by XLPE cable

3 Answers  


what is difference between differential protection and distance protection and how we calculate the sloop?

5 Answers   OPS, Power Grid,


A dc motor running on dc drive whose input is 3ph AC what will happen if we change the phase sequence of dc drive for e.g (R Y B) is connect as R B Y, will the motor run as same as previously running before changing phase without any effect

4 Answers  


current transformer balance the power level on both sides. e.g in case of step up, at secondary side voltage rise but current decrease and vice versa in case of step down transformer. but how this power level remains same in case of current transformer and voltage transformer

0 Answers  


WHAT TYPES OF OIL(STRUCTURE) ARE USED IN POWER TRANSFORMER INSULATION?

4 Answers  


What is Hi-Pot Test for Grid Station HV Equipments?

2 Answers   Siemens,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)