what will happen when power factor is leading in
distribution of power?
Answers were Sorted based on User's Feedback
Answer / jay pandya
i think if in a distribution line if pf becomes leading
then voltage leval increase so it can cause some damages to
the receiving side.
| Is This Answer Correct ? | 23 Yes | 2 No |
i think when the power factor at
distribution side increases, the recieving
voltage increases according to farranti
effect. But at recieving side we dont
require more than rated voltage. It can
damage the equipment by damaging the
insulation, which is not rated for that
much higher voltage....
| Is This Answer Correct ? | 12 Yes | 3 No |
Answer / sethu
The effects of lower power factors, no matter lagging or
leading, will have the same effects on the system such as to
increase the KVA rating of machines, increase the copper
losses, increase the cost of installation of conductors,
etc. In addition to the above, due to Ferranti effect, the
receiving end voltage will be higher than the sending end
voltage (ie) the voltage regulation will be positive.
| Is This Answer Correct ? | 11 Yes | 5 No |
Answer / salahudeen
dear frnds,
if pf leads then amount of power form sorce to
compensate reavtive power is very less & current value
reduced hence conductor size & swich gear size also reduced
for any clari
contact
| Is This Answer Correct ? | 16 Yes | 12 No |
Answer / cv
the load starts supplying reactive power to the grid if the
power factor is leading. it only means that the utility
will be applicable for benefits from the cesu.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / subhani
if power factor is leading then current leads
voltage.so,better regulation can be obtained to some extent
as it increases the receiving end voltage by compensating
the voltage drop caused by lagging reactance if any present
in the netwok as all the daily used loada are lag in
nature.no compensation of line wil b required.it ensures
stability of the system.
| Is This Answer Correct ? | 2 Yes | 4 No |
Answer / gova
When PF is leading,this will create a same problem like
lagging PF.
i.e current taken from source is increased
Cable size increased
loss increased
eff decreased
regulation poor
| Is This Answer Correct ? | 14 Yes | 19 No |
Answer / osayamwen osasre anthony
if theirs is high power factor, i.e if the power factor is
close to one:
1.losses in form of heat will be reduced,
2.cable becomes less bulky and easy to carry, and very
cheap to afford, &
3. it also reduces over heating of tranformers.
| Is This Answer Correct ? | 12 Yes | 19 No |
dear reader..,
if the pf is leading the
power system be smooth as
well as cost also decrease..
| Is This Answer Correct ? | 1 Yes | 11 No |
Answer / narayanan
I think power factor never become leading or more than 1,because cos has maximum value of 1
| Is This Answer Correct ? | 3 Yes | 15 No |
voltage at generation stage is usually- ? a.11kv b.33kv c.66kv d.220kv
In what cases (circumstances)we should apply P controller, PD controller, PI controller & PID controller ?
If AVR fails in DG set what will be the affect?
17 Answers GoodYear, Hotline Glass, HSL,
state the construction of incondenscent lamp?
While miss missed name platform fo electric motor how to calculate simple fourmul,?
what is difference between earth fault& restricted earth fault.
How are load losses and no-load losses measured at site in a DG set?
IN Electric train which type of motor is used,for what reason they uses?
How to calculate the current capacity of the 3C / 1C Al/Cu power cable???
in thermal power plant the steam produced is made to cool after falling on the turbine blades. my question is why this is done while the same is needed to heat up again. "jab pani ko wapis garam hi karna hai to thanda kyu karte hai"
how to commissioning the genset with amf panel?
which fault current is maximum: 3 phase short circuit, LG, LL or LLG?? why?? in one of the problems that i have solved, 3 phase short circuit current on an unloaded generator came out to be less than the LG fault current. can anybody please explain why.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)