Dear Sir,
we met a disaster with our 62.5 kva genset, after rewinding
we informed by our contract engg that due to return current
coming in neutral & impropper earthing this happend.
But after all set up & load balance we checked & found
again we have about 20 to 32 amp return current on neutral.
we have 12 airconditioner + 12 mini fridge on single phase
line.
Pl suggest any idea to solved this problem
Answers were Sorted based on User's Feedback
Answer / guru
Ground the neutral point of Genset and your problem will be
solved
| Is This Answer Correct ? | 5 Yes | 0 No |
Answer / sheikh
I think imbalance load is main reason of this problem and cross current compensation instrument transformer should be installed on your common bus bar to prevent this loss
but balance load all of 3 phase eleminate the highest neutral current.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / rishabh sharma
i think the load on your single
phase need to be distributed to all
three phases equally. this problem
occures due to load imbalance.
| Is This Answer Correct ? | 1 Yes | 1 No |
what are the major & minor faults that occur in an inverter and in UPS ? And how to repair and resolve them ?
How can we connect additional batteries to three phase ups? What are parameters we have to check when connecting?
2 Diesel Generators 900KVA connected to the bus bar for essential load as an alternative for power taken from 11/440V 3KVA Transformer supplying this bus bar. my question here is in the event of power failure on 11KV side can I feed the power to 11 KV bus by using the same transformer as reverse feed, what will be the inrush current???
What do you mean by screen of power cables?
What is meant by Floating Neutral? how to prent
Why transformer called by KVA?
can any tell me how to do wiring connection in L&T 3ph 4wire E301 CT operated energy meter, what is P1,P2,P3,P0. M1,M2,M3, L1,L2,L3.
2 Answers Bhartiya International,
Hello sir, pls send me hpcl technical test papers .i am. Appearing for the exam.
why voltage will come different in phase?
how much earth resistance consider to commissioning the transformer?
What are the causes of having an rmu explode after installation? And how do u treat the bushings of an rmu?
Why the design of electromechanical energy conversion machines is based on the medium of conversion as megnetic field not as electric field?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)