we met a disaster with our 62.5 kva genset, after rewinding
we informed by our contract engg that due to return current
coming in neutral & impropper earthing this happend.
But after all set up & load balance we checked & found
again we have about 20 to 32 amp return current on neutral.
we have 12 airconditioner + 12 mini fridge on single phase
line.
Pl suggest any idea to solved this problem
Answers were Sorted based on User's Feedback
Answer / guru
Ground the neutral point of Genset and your problem will be
solved
Is This Answer Correct ? | 5 Yes | 0 No |
Answer / sheikh
I think imbalance load is main reason of this problem and cross current compensation instrument transformer should be installed on your common bus bar to prevent this loss
but balance load all of 3 phase eleminate the highest neutral current.
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / rishabh sharma
i think the load on your single
phase need to be distributed to all
three phases equally. this problem
occures due to load imbalance.
Is This Answer Correct ? | 1 Yes | 1 No |
how braking & making capacity of circuit breaker is calculated?
at what rate the micro controller increment its timer....is it 1micro seconds or 1/(12*10^6) seconds
what is the criteria for selecting fuse rating in 1phase, 2phase & 3phase welding sets?
What is the difference between earth and neutral
4 Answers ABB, Tamboli Engineers,
What is a copper loss or i2r loss pc?
what is conductor copnstant of ab cable
What loads the lagging and leading effects comes in a circuit?
how to varied the frequency in transmission line and how i kept it as a constant one?
What are stable systems?
what do u understand from filter factor of reactor?
What's ND relay & it's functions?
why field winding is placed on rotor winding not on stator winding in case of synchronous machine?