i heard that power factor(PF) is the main concern for
industries, if they are maintaining PF around 0.6 they will
be fined for that. now the question is, how can they improve
the PF ranging between 0.9 to 0.95 which is safe for them
i,e escaping from the fine?
Answers were Sorted based on User's Feedback
Answer / sai
we can use the Requird rated capacitors while we can
mainten the pf
| Is This Answer Correct ? | 10 Yes | 1 No |
Answer / abdul wajid
Power factor in industries can be improved by using
capacitor banks
| Is This Answer Correct ? | 3 Yes | 0 No |
The PF is low because of inductive load. You can improve IT by adding capacitive load. Luckily cap load is loss free.That means you dont pay kwh for it but you must buy and maintain the capacitor and on and off it as necessary at the right amount.
One way to know how much you need, is you must know the load in KW and the pf.
assuming the load is 500 kw and the PF is 0.6 and you want to improve it to 0.95. you can find out the kva demands at this two pf levels
500/0.6=833kva . 500/0.95=526 kva, 833 kva -526kva =307kva
If you add 307kvar into the system in paralel you would improve the pf to 0.95 you can divide this into 8 steps of 40 KVAR each connected accros the 3 phases through an auto PF regulator.Your cap on each step will be rated as 40 kvar at 415 volts (rated voltage) 3 PHASE.
I welcome any improvements or comment about this.
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / amit biswas
inddustries mostly use static variable compensation (SVC)
technique for pf improvment.
Nowwhy dose pf drops? Due to inductive loads(eg.due to
arcing furnaces)
what SVC scheme dose is it proptionatly increases
captcitacne with inc. inductance or vice versa.
also using syc. motors can improve pf
(remember sync. motor is also called sync. condensor)
| Is This Answer Correct ? | 2 Yes | 2 No |
Answer / edy
Let say the load 500kw and u wanna increase ur power factor
from 0.6 to 0.95
500 (Tan 1-Tan 2)-u can use complex calculator to convert
from cos to tan
500 (1.33-0.32)
505kvar
u can set it with 6 step
505/6
84kvar and make it 80kvar each step
| Is This Answer Correct ? | 0 Yes | 0 No |
We have 11kV/110V three phase indoor potential transformer in 66/11kV Sub-station, where the failure of PT is frequently happening and the rating of the PT is 0.2 class accuracy, with primary star and seconday (two cores) star connected. Some experts has suggested to not to connect the PT Primary neutral to the ground because when transformer neutal NCT connection is loose; the faulty current will flow through the PT primary neutral, resulting into failure of PT. My question is: Is it necessary to remove the primary neutral connection of the PT from ground? if not, what would be the reason for failure of PT. Please guide me.
what is main difference between live tank and dead tank current transformer?
why starter use to on a motor
What about Reactive power.and role of that one?
What are the protections for safe running of electric generator?
What should be the height of basement according to NBCC code?
what is subtransient , transient and study state ac components
how dc load convert to ac load
all electricals questions
what is the benefit of floating our DC source? if i have two floating DC source of which 1 has a ref voltage of -21VDC and the other of -18VDC. can it be connected in parallel to share a common ref voltage? if not, how do i make both sources to be of common ref voltage? tks
how to check 3phase motor winding with help of multimeter?
if harmonics is generates on the secondary side of transformer then why we put LC ckt on prim side?(i m talking abt rectiformer transformer)
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)