i heard that power factor(PF) is the main concern for
industries, if they are maintaining PF around 0.6 they will
be fined for that. now the question is, how can they improve
the PF ranging between 0.9 to 0.95 which is safe for them
i,e escaping from the fine?
Answers were Sorted based on User's Feedback
Answer / sai
we can use the Requird rated capacitors while we can
mainten the pf
| Is This Answer Correct ? | 10 Yes | 1 No |
Answer / abdul wajid
Power factor in industries can be improved by using
capacitor banks
| Is This Answer Correct ? | 3 Yes | 0 No |
The PF is low because of inductive load. You can improve IT by adding capacitive load. Luckily cap load is loss free.That means you dont pay kwh for it but you must buy and maintain the capacitor and on and off it as necessary at the right amount.
One way to know how much you need, is you must know the load in KW and the pf.
assuming the load is 500 kw and the PF is 0.6 and you want to improve it to 0.95. you can find out the kva demands at this two pf levels
500/0.6=833kva . 500/0.95=526 kva, 833 kva -526kva =307kva
If you add 307kvar into the system in paralel you would improve the pf to 0.95 you can divide this into 8 steps of 40 KVAR each connected accros the 3 phases through an auto PF regulator.Your cap on each step will be rated as 40 kvar at 415 volts (rated voltage) 3 PHASE.
I welcome any improvements or comment about this.
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / amit biswas
inddustries mostly use static variable compensation (SVC)
technique for pf improvment.
Nowwhy dose pf drops? Due to inductive loads(eg.due to
arcing furnaces)
what SVC scheme dose is it proptionatly increases
captcitacne with inc. inductance or vice versa.
also using syc. motors can improve pf
(remember sync. motor is also called sync. condensor)
| Is This Answer Correct ? | 2 Yes | 2 No |
Answer / edy
Let say the load 500kw and u wanna increase ur power factor
from 0.6 to 0.95
500 (Tan 1-Tan 2)-u can use complex calculator to convert
from cos to tan
500 (1.33-0.32)
505kvar
u can set it with 6 step
505/6
84kvar and make it 80kvar each step
| Is This Answer Correct ? | 0 Yes | 0 No |
Why Neutral Earthing pits and body earthing is interconnected
Is potential difference materials property ..? if yes tnen how.. explain brifly.
What happen Grid EARTH plat got cut.
What are the advantages of using distance protection schemes as opposed to normal overcurrent/ earth fault protection on high voltage feeders.
How can i learn to programme every VFD. Or is there any typical study to understand VFD programming.
Why does the Solid state Rectifiers for 3-ph brake motors sometimes have 2 & sometimes 3 output terminals?
why phase to phase voltage are 290 rather then 440?
In chillers & freezers which gas will be use?
If u have 60KVA UPS, than tell me how systems ( computers ) u may connect?
What is the tension required for the 25000 CFM AHU belt
principle of power export and import in captive power plant.Is it depends upon voltage,current or frequency?Plz explain briefly.
what is high and low cut off voltage of BB and DG at SPS????????
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)