Why motor is not calculated in kva, whereas transormers are
calculated in kva
Answers were Sorted based on User's Feedback
Answer / electrical ravi
Normaly Source is rated in KVA where as appliance/Load is
rated in KW.
Transformer converts product of V1 X I1 into V2I2, there is
no lead or lag pf at no Load, so the manufacturer specify
the rating of the transformer in KVA.
In motor, the electrical energy is converted to mechanical
energy and there is losses within the unit and there is
phase difference between voltage and current and thus
forming a builin power factor. So the manufacturer of motor
specifies the rating in KW with powerfactor value on its
name plate.
| Is This Answer Correct ? | 9 Yes | 2 No |
In generation,transmission and distribution voltage frequency is either 50HZ or 60 HZ;why are only these frequencies?
What is K-rated transformer? What is the use of it? What can be the size(pls provide calculation if possible) of K- factor transformer for 550kW,690V motor operating with drive (VFD)?
What is the type of electrical earthing recommended in hard rock area
Define what is the function of anti-pumping in circuit breaker?
How to calculate the current in DG What are the type of power pls explain with related formulas
1 Answers Corona Enterprises, Sodexo,
Sir, why generating power plant operating at above 0.9 lag? detail explaination?
I try to check the three phase voltage in multimeter, in 125A isolator switch incommer. first i touch R phase, and then i touch Y phase using multimeter, the moment i touched, it blasts and that moment i got blindness. multimeter selector position is correct(750V AC MODE AND RED PROBE WASS IN v AND BLACK PROBE WASS IN COM. MODE. COULD ANYBODY GIVE ANSWER FOR THIS TO AVOID FURTHER ACCIDENTS PLEASE?
why are laminations used in constructing the field core?
At light load transformer efficiency is less because A secondary output is low B transformer losses are high C fixed loss is high compared to output D copper loss is small
what is the power ratio between power in star and delta circuit?
If the load of transformer is getting more than its rating,,,than how to overcome this problem? Suppose thee rating of transformer is 315kva and the load is going beyond than the rating say around load: 352kva... Than how can we solve this problem without deducting the load.
Differentiate between Zero and Negative sequence current
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)