MCCB 400 Amps 50KA 430Volt AC
What is mean by 50KA
Answers were Sorted based on User's Feedback
Answer / arun
50 KA is its short ciruit current at which it will
breakdown.
Is This Answer Correct ? | 54 Yes | 6 No |
Answer / gajajan kuhite
THE MEANING OF 50 KA IS THAT MAX. RATING OF BREAKER.MEANS IT
CAN WITHSTAND S.C. CURRENT UPTO 50 KA. WHEN S.C. CURRENT IS
GREATER THAN 50KA IT MEANS MCCB SHOULD NOT WITHSTAND & IT
MAY B DAMAGE.
Is This Answer Correct ? | 41 Yes | 3 No |
Answer / anil bhatia
50 KA is peak maximum curent or withstandind capacity of
MCCB upto which it will work or withstand, beyound this
limit it will damege .
Is This Answer Correct ? | 17 Yes | 0 No |
Answer / rajendran
Normally this 50 KA refers the Breaking capacity of the
circuit breaker
thanks
Is This Answer Correct ? | 15 Yes | 9 No |
Answer / yadlapalli suresh
50KA means withstandable capacity of the breaker,,the current crosses 50KA ,the breaker get damaged even it is in trip condition ,,then we replace it with new breaker. ok
Is This Answer Correct ? | 6 Yes | 0 No |
Answer / shakeel ahmed
50KA is the breaking capacity. which means that for all fault currents below 50KA, the circuit breaker can de-energize the circuit successfully. if the fault current comes more than 50KA then this circuit breaker will not be able to break, but itself will get damaged.
Is This Answer Correct ? | 3 Yes | 2 No |
Why we can not get 100% efficiency from a Gas Generator?
what will happen reduce the transformer voltage from 415v to 406v, is it save the energy,? are this methodis good to reduce the energy.?
Is a current transformer step up or step down ?
what is the principal of starting of a three phase induction motor.
what deffrence between KW $ KVA ?
how are reversing the direction of dc motor
How to calculate the cable size in sq. mm. when the load is given in KW?
Can we indroduce the principle of single phase induction mator to Transformer? i.e. by Producing rotating flux in the transformer.
Myself completed B.Tech ECE in private university but i am working as an testing and commissioning engineer in electrical field whether i am eligibility to apply electrical licence.
HOW DO I CALCULATE THE SETTINGS FOR THE DIFFERENTIAL PROTECTION OF A 12kV/6.6kV, 6MVA,DYN11 XMER WITH PRIMARY SIDE CTR 400/1 AND SEC SIDE CTR 600/1?
in ceiling fan and table fan what is the rotating part and what is the stationary part?
our company have 750 kva oil transformer.still we have facing a problem that is when voltage is 11.5 kv coming from HT side then LT-side voltage is 420v or above at tape 1.please give me best solution to decrease the voltage.