Answer / guest
May be the other side of the bus duct is grounded.........to
pass such a heavy current...........since it is already
grounded the buss duct offers very low resistance compared
to the human body.......
| Is This Answer Correct ? | 14 Yes | 4 No |
Answer / rupesh
as per my knowledge we will give a rated current of 2000a through low voltage high current source, not 415v. so the voltage is low then we will not get electric shock.
| Is This Answer Correct ? | 5 Yes | 1 No |
Answer / t eswara rao
First thing, the input voltage of the testing kit will be
415V but not the output of the testing kit. Please check
this and confirm.
Second thing, As said by rupesh, rated amphere of 2000A
will be fed by fixed low voltage and variable High current
source. So, you will not get the shock.
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / jivan gangawane
Generally this test is carried-out to verify the temp limits.
The testing done by applying low voltage to one end and
other end is shorted by suitable link same as that of heat
run test we conduct on transformers.
the capacity of test transformer is limited. Primary voltage
is high but the voltage on the secondary is less to a few
volts to circulate SC current.
So due to low voltage of the source, cuurent thru your body
will not flow due to low voltage.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / shivakumara
Dear it's very low voltage generally 5.5 or 10volt will apply and for full load rating of busduct,
One more thing is that we will short 3 termilas or busbars in HEAR RUN TEST, due to that temperature will rise upto stabilizing we need to check accordingly with standards that you referring IEEE or IEC
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / kaarthikrt&c09894209497
if u ground that bus bar during testing then wat test wil u
conduct on that?if d bus bar gets 2000A v can realize a
heat but wat about tat 415V,i wil anser soon...
| Is This Answer Correct ? | 2 Yes | 3 No |
Answer / aks
1) The Test set up will be isolated from the source through
isolation (Two winding)testing transformers .The test set
up will be floating and there is no return path to the
source .So you will not get shock by touching at a single
point.
| Is This Answer Correct ? | 2 Yes | 3 No |
how to measure the dc current?
Please define ampere?
i have flexible wire. size of conductors is 0.190 mm & no.of conductors are 48. then size of wire comes 1.37 sqmm instead of 1.5 sqmm . the what is tolerance for this size.
what do u understand from filter factor of reactor?
What is the technical difference between IS:1554 and Indian Railway IRS:S63/2007
why i can not use thimble on capacitor duty contactor
How to select cable rating for HT/LT Panels
what will happen when reverse reactive power occurs in alternators?
What is the main difference between generator and alternator
what are the main hormonics in ac?
how motor should be connected i.e star-delta or star-star or delta-delta ?
What are the special cables required for explosion proof wiring?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)