Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


During a temperature rise test of a bus duct, it is fed
with 415 volts at 2000 amperes. Why dont we get an electric
shock if we touch the bus bars?

Answers were Sorted based on User's Feedback



During a temperature rise test of a bus duct, it is fed with 415 volts at 2000 amperes. Why dont w..

Answer / guest

May be the other side of the bus duct is grounded.........to
pass such a heavy current...........since it is already
grounded the buss duct offers very low resistance compared
to the human body.......

Is This Answer Correct ?    14 Yes 4 No

During a temperature rise test of a bus duct, it is fed with 415 volts at 2000 amperes. Why dont w..

Answer / rupesh

as per my knowledge we will give a rated current of 2000a through low voltage high current source, not 415v. so the voltage is low then we will not get electric shock.

Is This Answer Correct ?    5 Yes 1 No

During a temperature rise test of a bus duct, it is fed with 415 volts at 2000 amperes. Why dont w..

Answer / t eswara rao

First thing, the input voltage of the testing kit will be
415V but not the output of the testing kit. Please check
this and confirm.
Second thing, As said by rupesh, rated amphere of 2000A
will be fed by fixed low voltage and variable High current
source. So, you will not get the shock.

Is This Answer Correct ?    3 Yes 0 No

During a temperature rise test of a bus duct, it is fed with 415 volts at 2000 amperes. Why dont w..

Answer / jivan gangawane

Generally this test is carried-out to verify the temp limits.

The testing done by applying low voltage to one end and
other end is shorted by suitable link same as that of heat
run test we conduct on transformers.

the capacity of test transformer is limited. Primary voltage
is high but the voltage on the secondary is less to a few
volts to circulate SC current.

So due to low voltage of the source, cuurent thru your body
will not flow due to low voltage.

Is This Answer Correct ?    0 Yes 0 No

During a temperature rise test of a bus duct, it is fed with 415 volts at 2000 amperes. Why dont w..

Answer / shivakumara

Dear it's very low voltage generally 5.5 or 10volt will apply and for full load rating of busduct,

One more thing is that we will short 3 termilas or busbars in HEAR RUN TEST, due to that temperature will rise upto stabilizing we need to check accordingly with standards that you referring IEEE or IEC

Is This Answer Correct ?    0 Yes 0 No

During a temperature rise test of a bus duct, it is fed with 415 volts at 2000 amperes. Why dont w..

Answer / kaarthikrt&c09894209497

if u ground that bus bar during testing then wat test wil u
conduct on that?if d bus bar gets 2000A v can realize a
heat but wat about tat 415V,i wil anser soon...

Is This Answer Correct ?    2 Yes 3 No

During a temperature rise test of a bus duct, it is fed with 415 volts at 2000 amperes. Why dont w..

Answer / aks

1) The Test set up will be isolated from the source through
isolation (Two winding)testing transformers .The test set
up will be floating and there is no return path to the
source .So you will not get shock by touching at a single
point.

Is This Answer Correct ?    2 Yes 3 No

Post New Answer

More Electrical Engineering Interview Questions

In an ideal transformer no load primary current I0 A lags behind V1 by 90 degree B is in the phase with V1 C leads V1 by 90 degree D lags V1 by 45 degree

1 Answers  


length of 4 core cable 95mm from substation LV VFD panel to Motor at field approximately 150 meter. Motor stop and power has been isolated from LV MCC ( Substation )to disconnect Motor for services. After Motor completed service propose to reinstall and reconnect Motor Cable, found earth cable sparkling during touching at metal / motor body. Inspect by clamp meter found earth cable have current flow AC 1-2amps and all earth cable at MCC LV also have current flow as same value. why it is happen?

2 Answers  


When to use Oil Transformer type and When to use Dry type? What is the difference between both?

2 Answers   ABC,


When in a large power system if the demand of power is larger than the generated power the frequency of the power system drops.(assume the rated frequency is 50Hz and now it is 49Hz) So does this mean the demand is totally supplied with a lower value of generated power in a lower frequency?

1 Answers  


What happened ,If 3 phase clearance not maintained in 33KV Line,11KV LIne etc?

0 Answers  


WHY SPEAKER OUTPUT IN WATTS??

2 Answers  


How to decrease or increase the range of voltmeter? can an ammeter be used to measure voltage? can a wattmeter used as voltmeter and ammeter?

3 Answers  


Which Programming software are use for Allen bradley PLC's?

16 Answers   ADC,


If a current -8+6sin6t is flowing three ammeter, one is a centre zero PMMC meter, one is true rms meter and one is moving iron meter. What are the reading of these three meter respectively?

0 Answers   National Insurance Company Limited,


It is observed that AVR of an Alternator is more likely to fail if the Generator and Mains Neutral are directly connected to each other. Why should this be so?

1 Answers  


What is the basis for selecting Vk/2 or Vk/4 for REF and Differential protection of Transformer and What is the significance of magnetising current

0 Answers   ABB, Jindal,


What is the difference between Earthing & grounding

4 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)