During a temperature rise test of a bus duct, it is fed
with 415 volts at 2000 amperes. Why dont we get an electric
shock if we touch the bus bars?
Answers were Sorted based on User's Feedback
Answer / guest
May be the other side of the bus duct is grounded.........to
pass such a heavy current...........since it is already
grounded the buss duct offers very low resistance compared
to the human body.......
Is This Answer Correct ? | 14 Yes | 4 No |
Answer / rupesh
as per my knowledge we will give a rated current of 2000a through low voltage high current source, not 415v. so the voltage is low then we will not get electric shock.
Is This Answer Correct ? | 5 Yes | 1 No |
Answer / t eswara rao
First thing, the input voltage of the testing kit will be
415V but not the output of the testing kit. Please check
this and confirm.
Second thing, As said by rupesh, rated amphere of 2000A
will be fed by fixed low voltage and variable High current
source. So, you will not get the shock.
Is This Answer Correct ? | 3 Yes | 0 No |
Answer / jivan gangawane
Generally this test is carried-out to verify the temp limits.
The testing done by applying low voltage to one end and
other end is shorted by suitable link same as that of heat
run test we conduct on transformers.
the capacity of test transformer is limited. Primary voltage
is high but the voltage on the secondary is less to a few
volts to circulate SC current.
So due to low voltage of the source, cuurent thru your body
will not flow due to low voltage.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / shivakumara
Dear it's very low voltage generally 5.5 or 10volt will apply and for full load rating of busduct,
One more thing is that we will short 3 termilas or busbars in HEAR RUN TEST, due to that temperature will rise upto stabilizing we need to check accordingly with standards that you referring IEEE or IEC
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / kaarthikrt&c09894209497
if u ground that bus bar during testing then wat test wil u
conduct on that?if d bus bar gets 2000A v can realize a
heat but wat about tat 415V,i wil anser soon...
Is This Answer Correct ? | 2 Yes | 3 No |
Answer / aks
1) The Test set up will be isolated from the source through
isolation (Two winding)testing transformers .The test set
up will be floating and there is no return path to the
source .So you will not get shock by touching at a single
point.
Is This Answer Correct ? | 2 Yes | 3 No |
If 110 volts ac is mixed up ith 12 volts dc what will be the resultant voltage and what is the wave form?
Why slip-ring and brushes are not required in squirrel cage induction motor?
If anyone would like to know or practice for FEWA papers contact me on mohamedrashad2@hotmail.com Just completed the supervisor exam in April 2021
HOW TO CALCULATE UPS BATTERY BACKUP TIME
HOW TO CHECK THE VECTOR GROUP OF A TRANSFORMER YD11?
differentiate PLC,DCS,SCADA?
How can calculate ups battery back up time?
25 Answers Cisco, Cooper, Pronet, Wipro,
What is the effect if power factor is above 1 or unity.
why dont we connect the two 12 V DC batteries in parallel, for an inverter (UPS)? is there any harm ?
why receiving end voltage increases in a system when capacitive load is added
What is the difference between electronic regulator and ordinary electrical rheostat regulator for fans?
sir i have applied for isro-09. still i did not got the HALL TICKET.