What is principal to reduce earth leakage current with
isolation transformer? When isolation transformer is
installed in input stage of system, earth leakage current
is reduced. the reason is why the leakage current of 2nd
stage of isolation transformer does not affect the 1st
stage's leakage current. I would like to know the reason.
As you know, earth leakage current is a kind of AC. So, How
to reduce earth leakage current in case that isolation
transformer is used?
Answers were Sorted based on User's Feedback
Answer / k.prakashchandra
If the neutral of secondary is not earthed ,the phases of
secondary lose the reference to earth ,but slightly for
capacitive coupling. After the second stage ,the earth is
almost completely isolated.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / wancheolkim
Hello K.prakashchandra,
If possible, please send me equivalent circuit for your
answer. I don't understand your answer fully.
Thank you very much.
wanceolkim@gmail.com
| Is This Answer Correct ? | 0 Yes | 0 No |
WHY TERTIARY OF POWER TRANSFORMERS IS LOADED WITH EQUIPMENTS LIKE CT,PT,ISOLATOR AND CB
What power factor maintain you maintain at u r organisation
What is mason's gain formula?
what happens when we give supply to the secondary of a transformer ?? for example 415v(pri)/110v(sec)
what is difference between KW,KVA,KVAR? also give me the formula for all the three...
how to carry out Magnetizing Current Test on Distribution transformer and what purpose we are doing this test.
what is meant by auto transformer?
what is the power factor of the megnetising component of transformer
1.where in India the maximum transmission voltage is operated? 2.what the methods are used to cool down the transformer?give the specific ratings of the transformer & specific cooling process. 3.how zero & negative sequence reactances are formed in a rotating machine when fault occur in the system?
What is the fullform of IPS in substaion using Aluminium Tubes
What are the symptoms of a bad PG card of a drive (inverter) esp. of Yaskawa Ac Drives (inverters) G7 ?
how i caculate the cable size for power factor correction unit for example 300kvar
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)