Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


WHAT IS THE USE OF ANTIPUMPING CONTACTOR IN HT BREAKERS

Answers were Sorted based on User's Feedback



WHAT IS THE USE OF ANTIPUMPING CONTACTOR IN HT BREAKERS..

Answer / felix

its nothing but an interlock for repetitive open/close

Is This Answer Correct ?    7 Yes 2 No

WHAT IS THE USE OF ANTIPUMPING CONTACTOR IN HT BREAKERS..

Answer / suresh chand

The main purpose of anpumping relay is to protect Circuit breaker in fault condition when CB is receiving direct closing command.
if a circuit breaker is reciving direct closing command or there is any shorting in its closing circuit and simultaniously there is in fault then the CB then the will close and trip many times and will damage its pole. by proving antipumping contactor/relay the VCB will not close electrical again untill closing pulse is removed. It contact also comes in series with closing circuit hence also act as a interlock in closing circuit.

Is This Answer Correct ?    3 Yes 0 No

WHAT IS THE USE OF ANTIPUMPING CONTACTOR IN HT BREAKERS..

Answer / ravendran

the relay used to protect the closing coil.that means
breaker closing condition again to give close command it is
used to bypass the command and save the closing coil.

Is This Answer Correct ?    3 Yes 1 No

WHAT IS THE USE OF ANTIPUMPING CONTACTOR IN HT BREAKERS..

Answer / rahul sharma

antipumping is a term itself sowing that prevention of
pumping . in antipumping when breaker had all ready closed
it will prevent to get other closing comand to coill. so
coill prevent from damage .

Is This Answer Correct ?    3 Yes 1 No

WHAT IS THE USE OF ANTIPUMPING CONTACTOR IN HT BREAKERS..

Answer / p dinesh

It is for the prevention of closure of breaker at faulty
condition

Is This Answer Correct ?    2 Yes 2 No

WHAT IS THE USE OF ANTIPUMPING CONTACTOR IN HT BREAKERS..

Answer / vinodg

Antipumping is preventing the continuos close/trip of
Circuit Breaker with single command during fault or
interlock trip exist.
ie Circuit breaker will close only once when trip signal
exist.

Is This Answer Correct ?    0 Yes 1 No

WHAT IS THE USE OF ANTIPUMPING CONTACTOR IN HT BREAKERS..

Answer / n.srinivasarao

IT is Protection of closing coil.

Is This Answer Correct ?    2 Yes 4 No

WHAT IS THE USE OF ANTIPUMPING CONTACTOR IN HT BREAKERS..

Answer / s.gowrisankar

MR.FELIX i say that it is only the interlock for
closing,opening won't come in to picture

Is This Answer Correct ?    0 Yes 4 No

Post New Answer

More Electrical Engineering Interview Questions

what is the relation between size of the anteena and wavelenghth of radiated wave

0 Answers  


what is the working principle of electrical motors?

4 Answers  


how it can be decided what will be the rating of CT and PT to be used in LT or HT cables?

3 Answers  


if there is fire alarm,what is ur activity?

4 Answers  


why high current produce in case of transformer when turns are internally gets shorted.

3 Answers   TCS,


What is different bewteen low or high impedance busbar protection scheme

0 Answers  


How reverse power relay sense the power is reverse in the system.

2 Answers  


on which power factor synchronous motor run

2 Answers   Bhel,


WHAT IS THE DIFFERENCE BETWEEN SHOP DRAWINGS/ DESIGN DRAWINGS AND AS BUILT DRAWINGS??

2 Answers   ACC, Al-Jaber, Dubai Group, ECEC,


RELAY 1. REF RELAY : • OPERATION WITH CT CURRENT FLOW DIRECTION. • WHY REF RELAY WHEN DIFFERENTIAL RELAY IS THERE. • REF RELAY STABILITY CHECK BY PRIMARY INJECTION – WHICH POINT FOR CUR RENT INJECTION. • WHY REF RELAY NEED STABILISING RESISTOR. IF RESISTOR SHORTED OR BYPASSED, WHAT WILL HAPPEN. • WHICH TYPE OF RELAY FOR REF, HIGH IMPEDANCE OR LOW IMPEDANCE. • IF NEUTRAL CT IS NOT CONNECTED IN THE CIRCUIT, WHAT WILL HAPPEN. • REF PROTECTION ACTS ON WHICH OF FOLLOWING: SINGLE PH. TO E/F; PH-PH TO E/F; THREE PH. TO E/F. 2. DISTANCE RELAY : • BASIC PRINCIPLE AND TYPES • SWITCHED MODE PROTECTION – WHY IS IT CALLED SO. • SCHEMES USED • WHY ZONE-1 SET AT 80% • SETTING RANGE FOR ZONE-2 AND ZONE-3 • HOW SINGLE PHASE TO GROUND FAULT MEASUREMENT IS DONE. • 3. WHAT IS POLARITY. CT LOCATION IF INTERCHANGED WHAT WILL HAPPEN. 4. SOLKOR RELAY: 1. WHY SOLKOR IS USED. 2. CIRCUIT DIAGRAM OF SOLKOR RELAY 3. DIFFERENT PARTS OF RELAY 4. HOW IT WORKS. 5. EXPLAIN BY VECTOR DIGRAM. 6. WHAT ADVANTAGE FOR USING SUMMATION TR. 7. DIFFERENCE BETWEEN R & RF WITH CIRCUIT. 8. ADJUSTMENT OF PADDING RESISTANCE. 9. WHAT IS LEAKAGE CURRENT AND HOW TO MEASURE. 10. WHAT HAPPEN IF LINK IS LEFT OPEN. 11. 5KV/15KV INSULATION TR. ARE USED IN WHICH SYSTEM. 12. WHAT PRECAUTION TAKEN DURING TESTING. Relay Page 1 of 5 13. PROCEDURE BEFORE TESTING AND AFTER NORMALISATION. 14. HOW RELAY IS TESTED IN LIVE CONDITION. 15. RANGE OF SPILL CURRENT ANS SETTING OF RELAY 16. IF MEASURED CURRENT IS 5MILLI AMPS, CAN RELAY OPERATE. 17. EACH FAULT APPROXIMATE VALUE OF PICK UP. 18. WHAT IS THE REASON SOLKOR-R MODE PILOT SHORTED CONDITION RELAY CURRENT PRESENT. 19. AFTER SHUTDOWN, WHY NEED TO OPEN SOLKOR PILOT, IF NOT WHAT WILL HAPPEN. 20. AFTER NORMALISING WHAT CURRENT TO BE MEASURED, WHAT IS ACCEPTABLE LIMIT. 21. WHAT HAPPENS IF PILOT OPENS FROM RELAY, WHEN FEEDER IS LOADED. 22. CAN WE USE THIS RELAY AS O/C OR E/F RELAY. 23. ANY RELAY OTHER THAN PILOT CABLE TYPE. 24. IF FEEDER TRIPS ON SOLKOR, WHAT TO DO. 25. WHAT HAPPENS IF PILOT POLARITY REVERSE. 26. WHAT HAPPENS WHEN CT SHORTED AT ONE END. 27. WHAT HAPPENS IF PILOT SHORTED – STATUS OF RELAY 28. WHAT HAPPENS TO RELAY ,IF POWER CABLE GETS OPEN. 29. WHAT HAPPEN IF PADDING RESISTOR IS SHORTED AT ONE END. 5. TR. DIFFERENTIAL: 1. CIRCUIT DIAGRAM 2. DIRECTION OF FAULT CURRENT. 3. WHEN THE FAULT IS IN ZONE AND OUT OF ZONE. 4. CT CONNECTION IN PY. AND SY. SIDE. 5. BIAS SETTING AND BIAS CURRENT. 6. WHICH BIAS SETTING USED IN TRS. FOR HIGHER TAPS. 7. PURPOSE OF RESTRAINING BIAS COIL. 8. WHY BIASING REQUIRED. 9. EXPLAIN IPCT, FOR EXAMPLE, DYN10 VECTOR GROUP. WHY MATCHING TR. USED. 10. WHY NEED 2ND HARMONIC BLOCKING DURING INRUSH. 11. WHICH HARMONIC IS MORE 2ND OR 3RD. 12. HOW TO AVOID FALSE TRIPPING IN DIFF. PROTECTION WHEN INRUSH CURRENT FLOW DURING TR. IS ENERGISED. Relay Page2 of5 6. DIRECTIONAL RELAY: 1. CIRCUIT FOR USE OF DIRECTIONAL PROTECTION SYSTEM. 2. WORKING ZONE / NON-WORKING ZONE. 3. HOW THE CORRECT DIRECTION OF FLOW OF CURRENT IS DETERMINED. 4. CT & PT CONNECTION DIAGRAM. 5. SETTING OF PHASE & EARTH FAULT ANGLE AND OPERATING REGION. 6. WHICH DIRECTION IT IS PROTECTING. 7. WHAT PROTECTION AVAILABLE FOR POWER TR. 8. WHY CT CONNECTION IS STAR, IF TR. WINDING IS DELTA. 9. DIFFERENCE BETWEEN REF AND DIFF. RELAY 10. WHERE IS O/C & E/F RELAY CONNECTED EITHER HV SIDE OR LV SIDE AND HOW E/F RELAY WORKS IF TR. WINDING IS DELTA CONNECTED. 11. IN DELTA WINDING OF TR., IF ONE WINDING IS CUT AND NOT EARTHED, WHICH PROTECTION WILL ACT. 12. IF DIFF. & REF RELAY ARE NOT WORKING, WHAT IS BACK UP PROTECTION IN TR. 13. WHAT IS PURPOSE OF NGR AND HOW STANDBY E/F RELAY WORKING, TESTING PRECAUTIONS IF COMMON NGR IS USED. 14. WHAT IS PROTECTIVE ZONE OF STANDBY E/F RELAY. 15. WHAT ARE PROTECTION AVAILABLE FOR FEEDER. 16. AFTER TR. IS NORMALISED, WHAT CURRENT TO BE MEASURED. 17. BUSBAR PROTECTION: a. BASIC PRINCIPLE AND DIAGRAM WITH CURRENT DIRECTION. b. WHY OVER LAPPING CT’S REQUIRED, IF NOT WHAT WILL BE THE EFFECT. c. WHY CT SUPERVISION REQUIRED, HOW TRIPPING IS AVOIDED, WHAT IS CT SUPERVISION SETTING VALUE. d. HIGH IMPEDANCE & LOW IMPEDANCE TYPE e. TEST PROCEDURE(STEP BY STEP) f. AFTER NORMALISING, SPILL CURRENT VALUE AND LIMIT. Relay Page3of5 18. CIRCUIT BREAKER FAILURE – FUNCTION, WHY NEEDED, HOW TRIPPING ARRANGEMENT. 19. WHY INSTANTANEOUS ELEMENT IS NOT USED IN THE NETWORK. 20. WHEN FEEDER IS LIVE AND BY MISTAKE LINE EARTH SWITCH IS CLOSED, WHICH RELAY OPERATES – O/C OR E/F. 21. DURING TR. SWITCHING ON, IF DIFF. RELAY IS BLOCKED BY 2ND HARMONICS, WHAT ARE THE OTHER PROTECTION IN SERVICE. 22. WHICH OF FOLLOWING PROTECTION OPERATES FAST, WHEN 11KV CABLE COMPARTMENT GET FLASH OVER: CABLE DIFFERENTIAL; OVERCURRENT & EARTH FAULT; ARC PROTECTION. 23. WHICH PROTECTION OPERATES WHEN ANY ONE OF THE OHL PHASE IS CUT AND HANGING, NOT TOUCHED WITH EARTH. 24. WHAT ARE DIFFERENT TTB ALARMS – HOW YOU KNOW THERE IS ANY ALARM. 25. WHAT IS CIRCULATING CURRENT AND HOW IT WILL COME. 26. IF ONE TR. TRIPPED ON DIFF. RELAY WHAT YOU WILL DO. 27. IF SUB-STATION TRIP ON BUSBAR PROTECTION, HOW YOU WILL RESTORE. 28. WHAT IS CT SATURATION. HOW IT IS CARRIED OUT. 29. D.C EARTH FAULT – HOW YOU WILL FIND OUT. Relay Page 4 of5 30. PILOT WIRE SUPERVISION – HOW IT WORKS 31. IN 11KV SWITCHGEAR DBB SCHEME, ONE E/F RELAY IS FAULTY IN ONE FEEDER AND THERE IS NO SPARE FEEDER – HOW YOU WILL NORMALISE THE FEEDER. 32. WHICH PROTECTION IS USED FOR LONG CABLE FEEDER 33. DIFFERENCE BETWEEN TRAFO. DIFF. AND CABLE DIFF. PROTECTION. 34. WHAT TYPE CHARACTERISTIC AVAILABLE FOR O/C AND E/F RELAY. 35. WHAT IS THE DIFFERENCE BETWEEN STATIC AND ELECTRO- MECHANICAL O/C RELAYS. 36. WHAT IS DEAD ZONE 37. HOW TRIPPING OF OTHER ZONE AVOIDED WHEN BUS SECTION CB IN OPEN CONDITION FOR DEAD ZONE FAULT. 38. IF OUT OF STEP ALARM COMES WHILE ALL TR. IN SAME TAP POSITION, WHAT YOU WILL DO. 39. WHAT YOU WILL DO IF AN 11KV FEEDER FAILED TO TRIP ON: O/C or E/F or SOLKOR. HOW YOU RESTORE THE SUPPLY. Relay Page 5 of5

2 Answers   KSEB, Siemens,


which type sylbuse involved

1 Answers   BMRCL,


Mention what are the different colors on wires indicates?

0 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)