i have 400/230v transformer and didnt done the neutral
eatrhing. i connected one lamp to one phase and neutral to
the earth. but the lamp is not glowing. again i connected
neutral to earth and repeated the same. then the lamp is
glowing. in the first condition i tested with a line tester
also, at that time the tesrer is glowing what is happening
i dont know can any one help me?
Answer / amit khamesra
Very Simplr. As second point of trafo sec ( 230 V ) was not
grounded the current did not get the return path upto the
source. In second attempt. the second terminal being
earthed, the current got the return path thru earth.Hence
the lamp glow.
Is This Answer Correct ? | 3 Yes | 0 No |
. How to calculate the Short Circuit Impedance in Transformer? How to calculate the Short Circuit Impedance in Transformer?
why and where we use early make & late break contacts in protection?
What is the type of earth fault protection used in battery? explain.
what is the difference between surge protection capacitor and surge arrestor
how we can differentiate a motor and a generator just by a glance?
why a fan starts rotating in the reverse direction when condenser gets damaged?
What is the minimum permissive IR value for LT & HT motor for safe starting?
During Starter Panel Com missing I Found The Main Incomer 40Amp MCB 10KA Trip When Motor Change Star To Delta Motor Rating 20HP BUT When We Use Same MCB To Other Motor It Does Not trip Or What Is Necessaries for Star Delta Starter MCB SFU MPCB OR MCCB And What are The Breaking Capacity of MCCB in the Motor above 15HP
single sphase energy meter measur
What Should be the rating of transformer used in 33KV substation?
How we can design a cable for a 3phase load.
While testing the 33KV Busbar by using Hipot kit, what should be the test voltage we have to apply?