What is the formula for calculating Transformer Losses &
Efficiency. I want to compare the Transformer efficiency at
different loading condition.
Answers were Sorted based on User's Feedback
Answer / kashifhabib
Efficiency = (Output/Input)*100
&
Output (KW)= KVA * Power Factor
Input = Output + Iron losses + Copper losses
Iron losses are due to Primary voltage so remains constant
can be calculated by open circuit test
Copper losses are due to secondary current I*I*R
can be calculated by short circuit test
Exp: Full load copper losses 800 W
1/2 load copper losses will be 200 watts
| Is This Answer Correct ? | 368 Yes | 101 No |
Answer / vinod parasa
Efficiency = (Output/Input)*100
output=(x)(KVA * Power Factor)
input=(x)(KVA * Power Factor)+(X)^2 copperlosses+core losses
the volue of x depend on load
x=1 for full load
x=0.75 for (3/4)th load
x=0.5 for half load
x=0.25 for quarter load
copper losses are variable losses and iron losses are
constant losses.
at the time of full load copperlosses=iron losse
Full load copper losses 800 W
half load copper losses=(X)^2 copperlosses
x=0.5 for half load
=(0.5)^2 *400
=0.25*400
half load copper losses=200
| Is This Answer Correct ? | 190 Yes | 85 No |
Answer / n.makali
POWER Transformer is 55MVA, 27/11.5KV ,efficiency =99.49
Find the Losses of Transformer
| Is This Answer Correct ? | 89 Yes | 35 No |
Answer / s.ravi
Efficiency =
(Output/Output+Iron losses+Copper losses)*100
Iron losses = No load test,
Copper losses = Short circuit test
Regulation = (Impedance voltage/Rated input voltage)*100
Impedance voltage = Short circuit test(Voltage drop)
| Is This Answer Correct ? | 59 Yes | 33 No |
Answer / prof dr lehaz kakakhel
go for two tests
open and short circuits tests
From the open, u compute the core power loss and from the
short, u get copper losses. then the formula is
efficiency = output/ (output + the above two losses)
SIMPLE
| Is This Answer Correct ? | 36 Yes | 19 No |
how to improve power factor correction?
How to connect frequency meter in metering circuit?(single phase and three phase frequency meter)phase to phase or phase to neutral
what are pilot cells
If the Brush of DC motor is shifted by 90 deg, then what happens to voltage and torque? Both voltage and torque are zero. how to justify the answer?
if the length, number of turns and area of coil are doubled then inductance of the coil becomes.?
12.5 tons a/c is their how much kva generator can recommend to the customer.
which bulb is greater iluminited, 60w and 100w are conected in series?
what is neutral ground resistance relay? how it is helpful in protecting system?
why fault current time duration is calculated for 1 minutes?
1 Answers Rockfort Engineering,
How to calculate incoming cable size for 33KV, 1MVA transformer.
What will happened if the neutral of the (star connected secondry) Xformer disconnected? (if its Above KVA rated one)
High voltage test procedure of in swgr board. why should measure millivolt drop on testing time?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)