What is the formula for calculating Transformer Losses &
Efficiency. I want to compare the Transformer efficiency at
different loading condition.
Answers were Sorted based on User's Feedback
Answer / kashifhabib
Efficiency = (Output/Input)*100
&
Output (KW)= KVA * Power Factor
Input = Output + Iron losses + Copper losses
Iron losses are due to Primary voltage so remains constant
can be calculated by open circuit test
Copper losses are due to secondary current I*I*R
can be calculated by short circuit test
Exp: Full load copper losses 800 W
1/2 load copper losses will be 200 watts
| Is This Answer Correct ? | 368 Yes | 101 No |
Answer / vinod parasa
Efficiency = (Output/Input)*100
output=(x)(KVA * Power Factor)
input=(x)(KVA * Power Factor)+(X)^2 copperlosses+core losses
the volue of x depend on load
x=1 for full load
x=0.75 for (3/4)th load
x=0.5 for half load
x=0.25 for quarter load
copper losses are variable losses and iron losses are
constant losses.
at the time of full load copperlosses=iron losse
Full load copper losses 800 W
half load copper losses=(X)^2 copperlosses
x=0.5 for half load
=(0.5)^2 *400
=0.25*400
half load copper losses=200
| Is This Answer Correct ? | 190 Yes | 85 No |
Answer / n.makali
POWER Transformer is 55MVA, 27/11.5KV ,efficiency =99.49
Find the Losses of Transformer
| Is This Answer Correct ? | 89 Yes | 35 No |
Answer / s.ravi
Efficiency =
(Output/Output+Iron losses+Copper losses)*100
Iron losses = No load test,
Copper losses = Short circuit test
Regulation = (Impedance voltage/Rated input voltage)*100
Impedance voltage = Short circuit test(Voltage drop)
| Is This Answer Correct ? | 59 Yes | 33 No |
Answer / prof dr lehaz kakakhel
go for two tests
open and short circuits tests
From the open, u compute the core power loss and from the
short, u get copper losses. then the formula is
efficiency = output/ (output + the above two losses)
SIMPLE
| Is This Answer Correct ? | 36 Yes | 19 No |
what is let through energy of mccb
Rules and standards of electrical control wiring ?
WHAT HAPPENED DC SERIES MOTOR FIELD WINDING OPEN. CAN POSSIBLE.
IF % IMPEDANCE OF A TRANSFORMER IS INCREASED FROM 5.8% TO 8% HOW MUCH THE EFFICIENCY OF THE TRANSFORMER WILL COME DOWN?
What do you mean by reach and reach the point of the relay?
Compare salient pole and cylindrical rotor machines.
how to calculate power factor rating according to load? please give the answer in simple language, i'm not electrical side
how to erect roof control panel?
How will calculate losses in an multi core Aluminium LT cable of different sizes & upto what length we can use a LT Cable ?
What is load curve?
How to confirm the Phase shifting Transformer VECTOR GROUP relation , as below ZNy11.45d10.45-ZNYy0.15d11.15
What is a current transformer?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)