how to amps calculate from 1KVA?
Answers were Sorted based on User's Feedback
Answer / pillay
1 KVA means 1000 volts amps for single phase calculations
1 KVA means 1000 volts amps x 1.732 for three phase
so for 240v single phase is 1000/240=4.16 A
SO FOR 3 PH @ 415 V= 1000/415/1.732=1.39A
SO FOR 3 PH @ 440 V= 1000/440/1.732= 1.31A
SO for easy average easy calculations you can take 1.35 AMPS
for 1 KVA for 3 p;h calculations
| Is This Answer Correct ? | 30 Yes | 0 No |
Answer / kuldeep
KVA= Rt.3 VI from this formula we can find out Current.
| Is This Answer Correct ? | 8 Yes | 1 No |
Answer / psk
1000/220=4.5 A for single phase
PF will come into picture only if it is in Kilowatt. This is KVA rating
| Is This Answer Correct ? | 1 Yes | 1 No |
Answer / janakiraman
kva is nothing but the voltage and current are directly
propotinal and there is no phase difference between them.
| Is This Answer Correct ? | 0 Yes | 1 No |
Answer / be1
KVA=S , so you should know that S=Rt.(R^2+Q^2)
S=P*pf ---- (pf means power factor)
S=U*I*pf but in 3 phases you have
S=Rt.3*U*I*pf
| Is This Answer Correct ? | 1 Yes | 3 No |
Why sip ring used in ac motor also why its not used in dc motor?
if harmonics is generates on the secondary side of transformer then why we put LC ckt on prim side?(i m talking abt rectiformer transformer)
State thevenintheorem?
What is floating voltage?
In what cases (circumstances)we should apply P controller, PD controller, PI controller & PID controller ?
What is the fault or needs to be done when frequency in ac drives is not changing?
figure of phasor diagram of transformer when full load or no load ?
if a motor is running at 1500rpm then how you can find its HP
Can we use HRC fuse inplace of semi conductor fuse ? What are difference between them?
I am having a 42KW 3 phase electrical heating furnace, heating element is 80/20 nichrome material, my connections is made in such a way that 2 star connection compromising 2 coils per phase so totally 12 coils, shall if i use it unbalanced star condition (instead of 2 group of 3 phase or 1 group of 3 phase, connecting 4 phases of 5 phases) what will be the consequences and is it acceptable?
why voltage drop will occurs in 3 phase line?
why transformer impedance measure in % (percentage)
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)