Answer / ritesh
actually setting of over load relay depends on the duty of
motor.if duty of motor is 2 then set relay at full load
current.if it is 2.1 then set relay at 10% higher then full
load current so on...........
| Is This Answer Correct ? | 9 Yes | 3 No |
125% of the motor full load current require for Overload relay.
| Is This Answer Correct ? | 6 Yes | 0 No |
Answer / bijay
RELAY SETTING REQUIRES TWO THINGS CURRENT AND TIME
CURRENT SETTING CAN BE UP TO 20 TO 30 % FOR SMALL MOTORS
AND UPTO 10% IN MV MOTORS.
BUT DONT FORGET FOR MUCH TIME U R OVERLOADINIG THE MOTOR.
TIME SETTING IS ALSO IMPORTANT...
THIS DETERIORATES ITS INSULATION
| Is This Answer Correct ? | 11 Yes | 9 No |
Answer / exxon
Is it safer to find out the spec about the motor winding
before deciding the overload relay settings. Every motor
manufacture has detailed spec. about is motor winding such
as insulation class:. Overloading the motor full load
current will deteriorates the insulation and winding life.
| Is This Answer Correct ? | 8 Yes | 6 No |
Answer / suresh
set the overload setting standerd draw currents 10% extra
but less than rated current
| Is This Answer Correct ? | 6 Yes | 9 No |
What should be the amps for a MV fuses for transformer 630kVA 20(10)/0.4 kV
why select the 3 phase power supply system in electrical system.
How to calculate Air conditioning capacity for a telecom BTS shelter?
Why is starter necessary for a three-phase induction motor?
37 Answers BMM, Essar, Hero MotoCorp, ITI, Maruti Suzuki, Supertech, Watt,
what is the diffrence between resistive , inductive and capactive load please explain with exmpels?
What is fault level?How it is calculated and how it is Expressed?
How to select the earthing transformer,for DELTA TO DELTA TRANSFORMER OR ALTERNATOR SIDE.Pls post your answers and calculation.
may anybody tell me the names of institute where plc programing course are conducted
How to select the rating of a CT used for REF protection. The rating can be of equal rating of Phase current or neutral current rating
How to connect a ELCB with contactor and relay ?
when meggering a 3ph,480v oil reservoir heater on a regen gas compressor, why do I get a reading to ground when meggering phase to ground? shouldn't it read opened or is there something that makes it read closed? on the same heater, when ohming, it reads open. thanx
what is the function of bearing in dc mchine" and where it is placed
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)