why 1 to 5 vdc is used for output measurment
Answers were Sorted based on User's Feedback
Answer / kandan
since we use 4 to 20ma transmission signal,the voltage drop
at the o/p is 1 to 5V.
In the O/P 250 ohm resistance is used.So when the signal is
4ma then 4*250=1V
when the signal is 20ma,then the O/P is 20*250=5V.
Is This Answer Correct ? | 46 Yes | 4 No |
Answer / ranjit mallick
Because upto 1 volt and 4ma the signal can be trigered due
to some earth leakage, bias malfunction, noise signal,
small magnetic interferance etc.Hence it is used as lower
tolerance to avoid unwanted triggering of the instrument
and can be termed as floating output.
Is This Answer Correct ? | 3 Yes | 0 No |
Answer / abdul hakkem
for analog arithmetic calculation can be done only by Voltage, thats way 4-20 mA is converted & taken as a voltage output
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / rajesh
Because of the Burden resistance of the Instruments/Load of
PLC are normally 250ohms
So Its Corresponding we will get 1 to 5V
Is This Answer Correct ? | 6 Yes | 12 No |
why we use by pas on a positioner? When can a by pass be not used on a positioner ?
selection criteria of control valve? and selection criteria of actuator explain in brief?
What is mean by AC voltage and DC voltage
what is dc moter.
0 Answers Jindal Steel and Power, Lupin,
I want to install analog type, flange mounted gas flow meter (line size - 2"), for CNG flow measurement.Kindly give some details of flowmeter or suppler name, available in India.
How to check range of DP Transmitter
please tell me how maintainence person shifted to good epc company/design company
what is difference between RTD and Thermocouple?
How can you convert an SR Flip-flop to a JK Flip-flop?
what is start up vent valve ? why it is used in boiler?
8 Answers ACC, Bhushan Power Steel,
what is flow equation of kg/hr to m3/hr
why we use casced loop