suppose one 11KV DG is running, when we start the DG it
will make only 600 to 700v only, because that time the AVR
is not connected in the circuit, when we switch on the
AVR , the AVR gives the supply to exciter assyembly and the
rotor of alternator gets more exciting current and this
rotor current cuts more flux and the main voltage
increases , when it reaches to 11000v , the AVR sense the
11 kv and it minimised the supply voltage to exciter.
so we can say that when AVR fails, the generator will not
make voltage .

Is This Answer Correct ?    15 Yes 5 No

if AVR fails in D.G set, what will be the effect?..

Answer / abdul ghani fatima fertilizer

Dear Friends.
If Generator is running in Island mode then it will be
tripped due to excitation failure so all the load will be
cut off, and if the Generator is running in Parallel even
then it will be tripped on under excitation.

But if the excitation protection fails then it will be
tripped on reverse power.

And if there is no any protection then during parrallel
running the faulty generator shall act as motor, and if
Generator running in Island mode it will be continuous run
without output rated voltage so loads shall not be
continued.

Is This Answer Correct ?    6 Yes 1 No

if AVR fails in D.G set, what will be the effect?..

Answer / ramji

Mr.Sudheer u r not clear.U r telling the condition after DG
starting only, not during running.
Mr.Shri can u please explain me how the voltage will be
fluctuating if the AVR is OFF.

In parallel mode if the AVR of the suspected DG
fails, then the reactive power of the particulat DG gets
reversed because the DG will be out of its running
quadrant.Since the reactive power is reversed, DG will be
trip on under reactance.Also if it is not tripped, its
outgoing current will be increased, so it will trip on Over
current.

In island mode if the AVR of suspected DG set
fails, then the loads connected to it will be thrown off
immediatly and the DG may trip on prime mover overspeed due
to sudden throw of load or undervoltage protection on DG.

Is This Answer Correct ?    6 Yes 2 No

if AVR fails in D.G set, what will be the effect?..

Answer / shri..

The voltage will not stable it will go up & down.

Is This Answer Correct ?    7 Yes 6 No

if AVR fails in D.G set, what will be the effect?..

Answer / bejoy

As described above bt Fkexiraj the generator runs as motor
when the 2 alternator are in parallel ie synchronous
panel.The points of ramji is correct

Is This Answer Correct ?    4 Yes 3 No

if AVR fails in D.G set, what will be the effect?..

Answer / nishad

Failure of AVR means AVR will not deliver the excitation voltage to the exciter stator winding. Hence, Exciter stator winding will not be able to generate any magnetic flux and there will be no any field voltage generate in exciter rotor winding and it will not feed any output voltage to rotating diode assembly. If the diode assembly fail to get the supply, it will not supply the voltage to the main rotor winding which used to make the main flux between main stator and main rotor, and as a result main stator winding will not generate any output voltage even if the DG continuous running.

Is This Answer Correct ?    1 Yes 0 No

if AVR fails in D.G set, what will be the effect?..

Answer / felixraj

in parallel mode it continue to run as motor(lag ct)
in island mode it trips due to u/v protection

Is This Answer Correct ?    5 Yes 8 No

Post New Answer

More Electrical Engineering Interview Questions

what is HI POT test

4 Answers   Suzlon,


substation+ plc system

0 Answers  


Why current transformer is earthed??

2 Answers  


WHAT MEANT BY SEVICE FACTOR?

2 Answers  


We have 2 no. 4MW DG set. and GEB supply. But, we running, only 1 DG set. when we done APFC/Power factor setting : 0.90, then winding temp. Low. but when setting done : 0.83, then Winding temp. increase. WHY Why ? ? ?, plz give me answer.

4 Answers  






1. What is the difference between ac induction motor and ac synchronous motor?

11 Answers  


WHAT DO U MEAN BY THERMAL OVER LOAD RELAY& WHERE THEY ARE BUSED

4 Answers   L&T,


what are different types of excitation in synchronous generator,what is the difference between them

3 Answers  


how electical engineer is related to apsrtc (general) post? if they ask a question in interview as why did u choose this job what shd be answer

0 Answers  


What is LT? And specify the range of voltage?

10 Answers   HSL,


What is difference between 220v/50Hz & 120V/60Hz?

8 Answers  


What are :- AC Distribution Board (Single & Double Front) DC Distribution Boards Distribution Board LT Breaker Panel.

0 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)