why overload relay is not tripped at time of starting of
motor allthough staring current is too high?
Answers were Sorted based on User's Feedback
Answer / r.c.tiwari
becouse at the time of starting motor take high current
very less duration & over load relay generaly made by
bymatelic contect elements.by matelic element take a time
for heating.so over load rely not trip at the time of
starting.
| Is This Answer Correct ? | 21 Yes | 2 No |
Answer / ikab
when motor starts high Inrush current flows,
Relays are made smarter/biased to sense this Inrush current
and wait to let this current vanished. Inrush current has 2nd harmonics components and this makes it easy to recognize this current from normal current.
| Is This Answer Correct ? | 6 Yes | 3 No |
Answer / simon peter
Since the starting I of the motor is high but the tripping value is rated onthe basis of short or earth fault occured.....
| Is This Answer Correct ? | 0 Yes | 2 No |
Answer / shalini
In a star delta connection, OLR will be placed in the
dealta side.
Starting current would be high during the star connection &
timer will be set to switch over from star to delta.
Once the delta connection is activated, the current would
be naturally less & therby OLR doesnot trip.
| Is This Answer Correct ? | 0 Yes | 3 No |
Answer / lokesh
As simple one, we are using the starters ( DOL, Star Delta)
liket that for this purpose.
So this starter will help to start the motor with reduced
starting current.
| Is This Answer Correct ? | 2 Yes | 15 No |
If ROC does not lies inside unit circle,then ? a) Fourier transform converges b) Z transform converges c) Hatly transform converges d) Colpit Transform converges.
How do i perform grounding of star point of Genset (400V) for making connection with step up transformer of DELTA-DELTA (400V to 20KV) ? while Genset itself has its own neutral and grounding bus bar inside genset breaker box whereas we have another neutral and grounding busbar in synchronizing panel next to genset at maximum distance of 6meter, would someone pls advice if we can only perform neutral grounding in synchronizing panel or should we ground neutral on both places inside genset breaker box and synchronizing panel.
WHY WE ARE DOING THE EARTHING IN A SYSTEM. SOME PEOPLE ARE TELLING FOR PROTECTION. WHAT PROTECTION GIVE ME THE CORRECT ANSWER.
what is the acceptable value of TAN DELTA and dissipation factor for 11kV, 1.75HP Motor?.
how can get electrical c licence.now i am working in spining mill , transformer capacity 2750KVA. SANCTION DEMAND 2250KVA. PLEASE ADVISE ME . MY CONTACT NO 09944226823
why 3 phase is converted into 2 phase using electronics circuit why not 2 phases are diresctly putted from the 3 phase transformer??
what are the main faults that occur in stabilizers? How they corrected and resolved ? Types of stabilizers ?
what is the diff. btwn. electronic regulator and ordinary rheostat regulator for fans?
What is working principle of ACB and VCB?
how many minutes or seconds taken by the transmission of electrical power from generating end to distributing end?
what is the role of reactive powerin transmission and distribution?
what is amf panel & how it is working
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)