How much voltage we get between two wire of 4 to 20 ma
output? Is this voltage up or down respectvice to 4 - 20
ma ?
Answers were Sorted based on User's Feedback
Answer / kiran
normally you gets 24-30VDC diretly connecting the volt
multimeter acroos it.
Also depends on the connecting the load resistance across
it.
E,g. When you are connected the 250 ohm load across it then
you get 1-5 volt or for 500 ohm 1-10 volt up & dowm
respective 4-20mA.
| Is This Answer Correct ? | 23 Yes | 4 No |
Answer / srinivasansureshkumar
yes, it is.
Better to verify transmitter power Vs load Graph.(TX
manufacturer Manual)
you will understand a lot about the question related then
just understanding the 4~20 ma in normal condition.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / ajay ugale
if we r using 250ohm resistor in parallel with the signal
we will get 1-5Volt DC i.e at 4ma we will get 1 volt and at
20 ma we will get 5 Volt.
| Is This Answer Correct ? | 2 Yes | 1 No |
Answer / sathish kumar
It depends on the resistor. For 4-20mA o/p 200ohm resistor
wants to use. For 4mA o/p is 0.8V and 20mA o/p is 4V. It it
exceeds 4.4V means it will be short cicuit. To avoid these
problem zener diode will be use across the resistor for to
protect the system.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / karthick
Transmitter required 5V for display the parameter
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / sagar
Between two wire of 4 to 20ma signal always we get 24 valts...there will minor change in it during 4 to 20
ma variation..
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / mail2noor.hyd
voltage is 0-10V
transmitter i/p supply (source) -24V
o/p -4-20mA/0-10V
we prefeered always current i.e 4-20mA,
b coz voltage travel a long
distance voltage will drop, so thats y we preffered
current i.e 4-20mA
voltage is 0-10V
from mail2noor.hyd@gmail.com
| Is This Answer Correct ? | 0 Yes | 3 No |
How we select the range of level transmitter in closed vessel ?
what is the control valve?how many types of control valves are there
6 Answers Chemin, Hindustan Zinc,
different between calibration range and instrument range ?
Area classification, Equipments, Gas groups, temperature classification, Ingress protection, Fire Extinguishers.
How to convert mmWc(mili meter water colam) to tph(ton per hour)?
how can check the loopchecking for valves?
Why only negative 24 vdc supply give in vibration measuring system.
What is surge in compressors? How to detect and control it?
in my plant 100% feedwater control v/v is air to close but due to instrument air fail,the valve opens but instead of drum level high its get tripped in low low drum level.the urv of level tx is 0 and lrv is -800.pls tell me the reason. for such behaviour.
What are the disadvantages of Human-Machine Interface (HMI)? atleast 3.
Difine flashing , Cavitaion & Noise? how to minimize these effects
how to online calibration of remote seal tx.
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)