If The RTD(PT100) Show .776 Kohm Resistance the Temperature of process fluid how much?
Answers were Sorted based on User's Feedback
Answer / nishat
T=(R-100)/.385
R=resistance
T=temperature
put the value u will get the answer
Is This Answer Correct ? | 10 Yes | 1 No |
Answer / mugil
Rt=Ro(1+at)
a=alpha (constant=0.0038)
Ro=(constant =100 ohm)
776=100(1+0.0038xt)
t=1178
Is This Answer Correct ? | 1 Yes | 2 No |