What is the difference between AMF panel and DG
Synchronization panel? please define the working of both
the panels?
Answers were Sorted based on User's Feedback
AMF Panel: is Auto Mains failure panel. When the EB power
goes off with a time delay signal will go to DG self
starter to start the DG. And when the EB power
resumes,after definite time delay stop signal goes to DG
and EB supply contactor will become ON.For a fraction of
time power will not be there for the utilities.
In synchronization, there is no outage of supply to the
utilities.When the incoming genset is to synchrinize with
the existing set,we've to match the magnitude of the
voltage, phase angle and the frequency and then only we've
to switch on the incoming set's breaker.
Is This Answer Correct ? | 85 Yes | 10 No |
Answer / bhupinder singh verma
AMF Panel: is Auto Mains failure panel. When the EB power goes off with a time delay signal will go to DG self
starter to start the DG. And when the EB power
resumes,after definite time delay stop signal goes to DG
and EB supply contactor will become ON.For a fraction of
time power will not be there for the utilities.
In synchronization OF DG SETS, When the EB power goes off with a time delay signal will go to DG self starter to start the DG AND WHEN THE LOAD REACH THE 90% CAPACITY OF THE DG-1 THEN THE DG-2 WILL START AND THE DG-2 gen-set is to synchronize with the existing DG-1 THEN ,we've to match the magnitude of the voltage, phase angle and the frequency and then only we've to switch on the incoming set's breaker. THATS WHY THE OUT PUT SUPPLY SUPPLY OF BOTH DG SET WILL RUN ON THE SAME COMMON BUS BARS ( MEANS- DG-5OO KVA / DG-2 380 KVA THEN THE TOTAL LOAD IS 780 KVA ON COMMON BUS BARS ) IN THIS WAY WE CAN SYN. ELECTRICAL CITY BOARD POWER AND DG POWER ALSO.
Is This Answer Correct ? | 8 Yes | 1 No |
Answer / ajith kumar.s
1 st answer is right
but synchronization of palel is deffernt types one is rpm
synchronizing other is voltage and phase sequency this
uesed dark lamp or synchrocape used,
Is This Answer Correct ? | 11 Yes | 13 No |
why electron flow is opposite to current flow?
can volts/Hz be relied upon to use 460v,60Hz electric motors on a 380v,50Hz power supply?
How to calculate PF capactors for a connected load?
how could we calculate the no of outgoings from a 800 watt distribution board
what is earthed and inearthed cable or system?
WHAT IS BASICS TO SELECTION OF 11 kv Trasformer, send any calculation sheet for selection of transformer
In layman terms, what is the difference of Dielectric strength and dielectric constant when speaking of an insulating oil
what will be fault level of 11 KV , 2000 A ELECTRICAL SYSTEM?
What is the need of generator relay panel
what should be 3phase motor capacity or rating to connect in star connection. what should be 3phase motor capacity or rating to connect in delta connection. what should be 3phase motor capacity or rating to connect in star delta connection
why capacitor bank is not used in generator power
wht is an AVO metre. and whre it is used?