What is the difference between AMF panel and DG
Synchronization panel? please define the working of both
the panels?
Answers were Sorted based on User's Feedback
AMF Panel: is Auto Mains failure panel. When the EB power
goes off with a time delay signal will go to DG self
starter to start the DG. And when the EB power
resumes,after definite time delay stop signal goes to DG
and EB supply contactor will become ON.For a fraction of
time power will not be there for the utilities.
In synchronization, there is no outage of supply to the
utilities.When the incoming genset is to synchrinize with
the existing set,we've to match the magnitude of the
voltage, phase angle and the frequency and then only we've
to switch on the incoming set's breaker.
| Is This Answer Correct ? | 85 Yes | 10 No |
Answer / bhupinder singh verma
AMF Panel: is Auto Mains failure panel. When the EB power goes off with a time delay signal will go to DG self
starter to start the DG. And when the EB power
resumes,after definite time delay stop signal goes to DG
and EB supply contactor will become ON.For a fraction of
time power will not be there for the utilities.
In synchronization OF DG SETS, When the EB power goes off with a time delay signal will go to DG self starter to start the DG AND WHEN THE LOAD REACH THE 90% CAPACITY OF THE DG-1 THEN THE DG-2 WILL START AND THE DG-2 gen-set is to synchronize with the existing DG-1 THEN ,we've to match the magnitude of the voltage, phase angle and the frequency and then only we've to switch on the incoming set's breaker. THATS WHY THE OUT PUT SUPPLY SUPPLY OF BOTH DG SET WILL RUN ON THE SAME COMMON BUS BARS ( MEANS- DG-5OO KVA / DG-2 380 KVA THEN THE TOTAL LOAD IS 780 KVA ON COMMON BUS BARS ) IN THIS WAY WE CAN SYN. ELECTRICAL CITY BOARD POWER AND DG POWER ALSO.
| Is This Answer Correct ? | 8 Yes | 1 No |
Answer / ajith kumar.s
1 st answer is right
but synchronization of palel is deffernt types one is rpm
synchronizing other is voltage and phase sequency this
uesed dark lamp or synchrocape used,
| Is This Answer Correct ? | 11 Yes | 13 No |
What is an exciter and how does it work?
7 Answers FCUK, Lotte Chemical Titan, TATA,
If a 3 phase induction motor is in off condition in the conveyor and rotor of the motor keeps moving with the conveyor than the resistance of windings of motor varies. why is it so ??
How can we get electric power from lighting ?
what happen if drive input fail momentry at 48.5 HZ frequency?
How to know the back up time for a 5KVA UPS which is connected to 15 nos. of computers? Is there any formula for this? pls. tell me.
what could be the reason of a burnt current transformer in an electrical panel
gas turbine genrator reactances
onan full form
sir i have cleared the apti test of EIL held on 15th march and my interview will be in new delhi on 2nd june.i will be very much helpful if u help me regarding the type of interview questions comes at EIL.(URGENT.........PLZZZZZZZZZZ...............)
Differentiate between power relay and reverse power relay?
How much the fault level of 11 k.v.,22 k.v., 33 k.v. (in Maharashtra- M.S.E.D.C.L) for calculation of short circuit current & selection of h.t.cable.
What are the advantages of stationary armature and rotating field system?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)