What is the difference between AMF panel and DG
Synchronization panel? please define the working of both
the panels?
Answers were Sorted based on User's Feedback
AMF Panel: is Auto Mains failure panel. When the EB power
goes off with a time delay signal will go to DG self
starter to start the DG. And when the EB power
resumes,after definite time delay stop signal goes to DG
and EB supply contactor will become ON.For a fraction of
time power will not be there for the utilities.
In synchronization, there is no outage of supply to the
utilities.When the incoming genset is to synchrinize with
the existing set,we've to match the magnitude of the
voltage, phase angle and the frequency and then only we've
to switch on the incoming set's breaker.
Is This Answer Correct ? | 85 Yes | 10 No |
Answer / bhupinder singh verma
AMF Panel: is Auto Mains failure panel. When the EB power goes off with a time delay signal will go to DG self
starter to start the DG. And when the EB power
resumes,after definite time delay stop signal goes to DG
and EB supply contactor will become ON.For a fraction of
time power will not be there for the utilities.
In synchronization OF DG SETS, When the EB power goes off with a time delay signal will go to DG self starter to start the DG AND WHEN THE LOAD REACH THE 90% CAPACITY OF THE DG-1 THEN THE DG-2 WILL START AND THE DG-2 gen-set is to synchronize with the existing DG-1 THEN ,we've to match the magnitude of the voltage, phase angle and the frequency and then only we've to switch on the incoming set's breaker. THATS WHY THE OUT PUT SUPPLY SUPPLY OF BOTH DG SET WILL RUN ON THE SAME COMMON BUS BARS ( MEANS- DG-5OO KVA / DG-2 380 KVA THEN THE TOTAL LOAD IS 780 KVA ON COMMON BUS BARS ) IN THIS WAY WE CAN SYN. ELECTRICAL CITY BOARD POWER AND DG POWER ALSO.
Is This Answer Correct ? | 8 Yes | 1 No |
Answer / ajith kumar.s
1 st answer is right
but synchronization of palel is deffernt types one is rpm
synchronizing other is voltage and phase sequency this
uesed dark lamp or synchrocape used,
Is This Answer Correct ? | 11 Yes | 13 No |
what the purpose of transmited high voltage in over head lines
What is the suitable transmission voltage?
what is the significance of per unit impedance ?
sir please tel me how calucalte kwh if home taken load 30ams how maney kwh taken per day.and 3phase motor 5hp per hars how maney load teken and how mach kwh and forward me to electrical table for calicalte kwh and kvr and kvah
How to calculate Earth busbar size & what is the procedure we make for determine that?
WE are using a 63A MCCB(SIEMENS MAKE) for one of the feeder in LV substation panel.It is supplying to a lighting & power socket DB.Settings in the MCCB is Ir = 63 * 1 , Isd = 8 times of Ir , tsd = 0.5 sec( I2 t off). Sometimes this MCCB is tripping .But no trip in DB MCB. Can anybody tell me reason ? From where i can know about the MCCB settings?
if we convert Ampers into kva,which one formula use by us,pls tell me?
if d gen is 50kw,load is 60 kw,hw d gen ll supply d remaining power?
Zone of protection and tripping scheme of arc protection relay.
how would you determin the horsepower of a motor without a nameplate
Explain what is CBCT.
why the generating / transmitting voltage is in the order of multiples of 11(ie 11kv,22kv,33kv......)