How to know the back up time for a 5KVA UPS which is
connected to 15 nos. of computers? Is there any formula for
this? pls. tell me.



How to know the back up time for a 5KVA UPS which is connected to 15 nos. of computers? Is there a..

Answer / k.prakashchandra

Back up time is decided by batteries and the load.The
formula is simple. B/U time in hrs = stored energy in
batteries (AH x V(both of each battery) X Number of
batteries)/Load in Watt

Is This Answer Correct ?    3 Yes 1 No

Post New Answer

More Electrical Engineering Interview Questions

what is power factor?

3 Answers  


What is C2-M2-E2 class in circuit breaker. why and where it is to be used in circuit breaker

1 Answers  


The inventer is a battery, but if lost current at home u will turn on the fan but the is AC and inventer battery is dc . Then how the fan was rotating. What device Or machine in fan converst the Dc power to Ac power

0 Answers  


WHAT WILL BE THE SPEED OF MOTOR IF NO.OF POLES ON STATOR ARE NOT EQUAL TO NO. OF POLES ON ROTOR.???

4 Answers  


we have 1000 litre water tank,it located at 25m hight from ground level,the water level on 10m below from ground level.for fill the tank within 1 hour,how much of motor rating(HP) want to select?

0 Answers  






Describe Non I.S. Earth System and why is it used?

0 Answers   KPJV,


Why the frequency of a system is changed if the load changes?

5 Answers  


i want to know how to calculate the battery capacity based on the UPS . ex i want to run have one kva UPS Which should run 10 hours ? in that case how many batteries to be installed and what will be the AH Value .

2 Answers  


I have a reading off 1.5ohms at my mem my main c/b is rated at 40/6 amps in a domestic house and i was told to change it to a b curve c/b is this ok

0 Answers  


why ht motor connection in star

10 Answers   Suzlon,


length of 4 core cable 95mm from substation LV VFD panel to Motor at field approximately 150 meter. Motor stop and power has been isolated from LV MCC ( Substation )to disconnect Motor for services. After Motor completed service propose to reinstall and reconnect Motor Cable, found earth cable sparkling during touching at metal / motor body. Inspect by clamp meter found earth cable have current flow AC 1-2amps and all earth cable at MCC LV also have current flow as same value. why it is happen?

2 Answers  


If we have use two power cable for incomer, that time how many use cbct for earth leakage protection? 1 or 2 if 1 way? If 2 way?

0 Answers   REM Electromech Pvt Ltd,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)