what is the working difference b/w softstarter and
Variable frequency drive ?
Answers were Sorted based on User's Feedback
Softstarter can control the motor only at the starting
time, during running time it will be by-passed! but VFD's
can be used both to start as well as to control the speed
of the motor while its running!!
| Is This Answer Correct ? | 30 Yes | 1 No |
Answer / senindra123
soft starters is using for smooth starting only which will
be by paseed while running.
variable frequency drives are using for smooth atarting and
running. while running we can control the speed of the
motor also.
| Is This Answer Correct ? | 18 Yes | 0 No |
Answer / satyanarayana gupta
the main function of variable frequency drive is to
control speed of the motor according to the load it just
works as control system with feedback according to that
feed back it will change its speed
where as soft starter it will
just monitor the speed at starting time only
by using vfd's most of power consumtion is reduced
| Is This Answer Correct ? | 3 Yes | 1 No |
Answer / muhammad ashraf
Softstarter can control the motor only at the starting
time, during running time it will be by-passed! but VFD's
can be used both to start as well as to control the speed
of the motor while its running. and also VFD is control the
current of the motor.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / pardeep.kumar/hoshair pur/
Dear All,
VFD variable frequency drive means it will operate as per
our selected accelration de accelationa nd torque boost.
And Soft starter is device which will limit our starting
torque also.
Its majour application is in textile,A motor of 50 hp
connected to 150 spindles in which thread is unwinding from
samll cone to big cone,if it will start by a normal vfd or
direct start then due to large torque in starting as per
induction motor charecterstics,all thread will get broken.
But due to Softstarter it will limit the starting torque.
Soft starter limits the torque by limiting its current and
voltage. thats all.
| Is This Answer Correct ? | 5 Yes | 6 No |
what is the calculation formula for motor starting torque,running torque, running torque.
If load is 240 kw & pf is 0.8 lagging, than how to increase it from0.8 to 1.0(unit),which rating capacitor used, please give me Calculation. What is effact of consumer & suplier if pf is lagging or leading with on effect machines/ TF/GE etc.
what is the necessity of neutral in 3 phase system?
difference between isolater and circuit breaker?
what is kvarh? Please define it With calculation General motors ?
why do we need to use 3c+3e cable, normally i select only 3c+e cable and i think it is enough. pls explain the usefull of 3e cable ( in this project the earthing system is well done)
why florescent light was flickering?
why do power factor in the three phase induction motor increases with the load ???.
How can we parallel two transformer with vector gorup YNd11 and YNd1?How is connection two transformer GT?
what is the difference between changer, converter and transformer?
1. When do you use a VFD motor? 2. If the ceiling fan is on slow speed, does it consume less electricity? 3. If we want the fan to consume less electricity at low speed, what do we have to do? 4. What does “battery of 180 AMP HOUR” mean to you? 5. What does “battery of 180 AMP HOUR” mean to you? 6. If you don’t have coal, salt and copper, then how would you earth your connection temporarily at a camp site.?
6 Answers Asian Power, Bhel, Focus, Focus Energy, L&T,
why do we provide metallic enclosure to bus duct and then ground it?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)