what is the working difference b/w softstarter and
Variable frequency drive ?
Answer Posted / satyanarayana gupta
the main function of variable frequency drive is to
control speed of the motor according to the load it just
works as control system with feedback according to that
feed back it will change its speed
where as soft starter it will
just monitor the speed at starting time only
by using vfd's most of power consumtion is reduced
| Is This Answer Correct ? | 3 Yes | 1 No |
Post New Answer View All Answers
What is “pu” in ee?
what is the effect of change in supply frequency on load angle of synchronous motor,all other parameters remaining same?
11KV AND 22KV NETWORK KW CAPACITY IN RING AND RADIAL?
Proviiding the Dedicated N earth and individual Body Earths ,Finally these all looped /Now my Question :- will it not harm in case of Transformer Fault current flows in Dediacted N Earthing to Looped Body Earthing.
Is the installation of the filter cloths necessary before spreading the gravels at the transformer yards?
How much should be the load percentage for 15kva Inverter and Iinut & I output load with Calculations
What is the angle of inclination for the oil connection from transformer conservator to Bucholz relay and why?
How many methods use the load flow solution?
Why neutral cable carry current.
What are the advantages of autotransformer?
what is the formula for computing cable tray size & capacity
oltc of a transformer, how it works? and what are the equipment consist of describe briefly?
two phases with neutral supply can be taken in 3C X 10 sq.mm cable .
at what basis/standard we have to arrive the current density of aluminium/ copper in busbar?
How I calculate the ELCB for circuit breakers?