how to calculate the size of cable for 100 kva load,?can somebody tell me with a formula..

Answer / virendra

Considering Powe factor 0.8
Kw = KVA*.08
KW = 100*0.8
= 80 KW
w = 1.73 * 415 * Il * 0.8
80000 = 1.73 * 415 * I1 * 0.8
I = 80000/ 1.73*415*0.8
= 139 Amp

You can choose the cable which current carring capacity per
phase is on or above 140 Amp

By considering the future expansion of load the 180 Sq.mm
AYFY cable is ideal.

Is This Answer Correct ?    18 Yes 2 No

how to calculate the size of cable for 100 kva load,?can somebody tell me with a formula..

Answer / prashant singh

KVA=uder root3*V*A/1000
A=Under root 3*415*KVA/1000

Is This Answer Correct ?    22 Yes 7 No

how to calculate the size of cable for 100 kva load,?can somebody tell me with a formula..

Answer / abdulsubur

WE CAN GET FROM THIS REALTION
KVA=KW/KVAR
100*85=85KW
THEN FIND CURRNET FROM P=ROOT 3 VICOSPHI FORMULA THEN FIND
CURRENT AND THEN LENTH FROM THE MV=VD*1000/L*I

Is This Answer Correct ?    11 Yes 6 No

how to calculate the size of cable for 100 kva load,?can somebody tell me with a formula..

Answer / brijesh shakya

Before calculating size of cable, phase & voltage should be
clear then after we can calculate the current of load by
this formula
P=root3*V*I
I=P/(root3*V)
Accodingle we can select the size of cale.

Is This Answer Correct ?    8 Yes 3 No

how to calculate the size of cable for 100 kva load,?can somebody tell me with a formula..

Answer / jack

Depends on what voltage you working with.

P = V*I

You got P and V, find what your I is.

Then use a cable selection book from, eg. Olex, choose your
cable from there.

Is This Answer Correct ?    7 Yes 14 No

how to calculate the size of cable for 100 kva load,?can somebody tell me with a formula..

Answer / jiwanjot

i think something is wrong with question ...load can never
be in KVA it should in kw if we talk about motor.....

Is This Answer Correct ?    5 Yes 15 No

how to calculate the size of cable for 100 kva load,?can somebody tell me with a formula..

Answer / mehul g. c.

if your load is single phase then you should use 3.5c x 185
sq.mm alu. Armoured cable.

Is This Answer Correct ?    1 Yes 12 No

Post New Answer

More Electrical Engineering Interview Questions

Why HT motors are connected in star.

7 Answers   GIL,


How we can design a cable for a 3phase load.

1 Answers  


when we catch any one of the phases with our both hands in air(without touching ground),our body acts as a conductor.is it correct.please clarrify it.

4 Answers  


reason of capacitor failure or low voltage in alternator wtih 10kva dgset

0 Answers   adag,


Refernce currents are to be generated using refernce cueernts how can this be done??

0 Answers  






technically, what is the reason behind starting the motor star the delta connection .. and what other ways to do this rather than using " star-delta transformer"

0 Answers   Wipro,


when we supply in primary side of transformer then the supply goes in secondary side?how it works?

4 Answers  


Why restricted earth fault protection is needed? Why can’t differential Protection is sufficient?

1 Answers  


if 50hz transformer is required to be run on 50% frequency what needs to be done???????????

6 Answers   century,


do we people experience any shock if we catch any one of the three phases (R Y B)in air with out touching ground.

7 Answers  


Which test will be more severe for VCB?

0 Answers   CPRI, Reliance,


Give details of your interested designation, the post you are interested to serve the company better and explain why you think you can serve the company better in such position if employed?

0 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)