Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


how to calculate the size of cable for 100 kva load,?can
somebody tell me with a formula

Answers were Sorted based on User's Feedback



how to calculate the size of cable for 100 kva load,?can somebody tell me with a formula..

Answer / virendra

Considering Powe factor 0.8
Kw = KVA*.08
KW = 100*0.8
= 80 KW
w = 1.73 * 415 * Il * 0.8
80000 = 1.73 * 415 * I1 * 0.8
I = 80000/ 1.73*415*0.8
= 139 Amp

You can choose the cable which current carring capacity per
phase is on or above 140 Amp

By considering the future expansion of load the 180 Sq.mm
AYFY cable is ideal.

Is This Answer Correct ?    18 Yes 2 No

how to calculate the size of cable for 100 kva load,?can somebody tell me with a formula..

Answer / prashant singh

KVA=uder root3*V*A/1000
A=Under root 3*415*KVA/1000

Is This Answer Correct ?    22 Yes 7 No

how to calculate the size of cable for 100 kva load,?can somebody tell me with a formula..

Answer / abdulsubur

WE CAN GET FROM THIS REALTION
KVA=KW/KVAR
100*85=85KW
THEN FIND CURRNET FROM P=ROOT 3 VICOSPHI FORMULA THEN FIND
CURRENT AND THEN LENTH FROM THE MV=VD*1000/L*I

Is This Answer Correct ?    11 Yes 6 No

how to calculate the size of cable for 100 kva load,?can somebody tell me with a formula..

Answer / brijesh shakya

Before calculating size of cable, phase & voltage should be
clear then after we can calculate the current of load by
this formula
P=root3*V*I
I=P/(root3*V)
Accodingle we can select the size of cale.

Is This Answer Correct ?    8 Yes 3 No

how to calculate the size of cable for 100 kva load,?can somebody tell me with a formula..

Answer / jack

Depends on what voltage you working with.

P = V*I

You got P and V, find what your I is.

Then use a cable selection book from, eg. Olex, choose your
cable from there.

Is This Answer Correct ?    7 Yes 14 No

how to calculate the size of cable for 100 kva load,?can somebody tell me with a formula..

Answer / jiwanjot

i think something is wrong with question ...load can never
be in KVA it should in kw if we talk about motor.....

Is This Answer Correct ?    5 Yes 15 No

how to calculate the size of cable for 100 kva load,?can somebody tell me with a formula..

Answer / mehul g. c.

if your load is single phase then you should use 3.5c x 185
sq.mm alu. Armoured cable.

Is This Answer Correct ?    1 Yes 12 No

Post New Answer

More Electrical Engineering Interview Questions

What is LOP Sensor in DG??????

7 Answers   Emerson,


explain Uninterrupted power supply detailed electronical operation with circuit diagram

1 Answers   Emerson,


What are the rating wise protections required for Generators from 600KVA to 2000KVA

3 Answers  


In my project i am layout cables under the Maintainance bay /Maintainance yard in the TG Building. Whether in this route i can lay the H.T.Cables??? i am taking all H.T cables from the H.T Transformer to the TG Building..

1 Answers  


I have 4 DG set with 1500KVA rating. system breakers are 11KV & alternator are 415 Volts. Between alternator & breaker one stepup transformer used. i want to Know what is max. resistance for body earthing & 415 & 11KV V Neuteal earthing. my fault current is 14 times for 2 sec.

0 Answers   Jindal,


where do we connect tap of tap changer, to H.V. side or L.V.side? and why?

5 Answers   Vedanta,


A 230V dc shunt wound motor has an armature resistance of 0,15&#8486;.When operating on no load at 650 rev/min the armature current is 6A . The motor takes a full load current of 85A. Calculate the full load speed if the field flux is (i) maintained constant (ii)reduced by 0,03

0 Answers  


what will happen if we directly give supply to rotor of a induction motor?

1 Answers  


what are the components of a start and stop motor control?

2 Answers  


what is use of substation? Any book on how to instal or construction of substations?

6 Answers   Siemens,


can you use 400 volt 3 phase and neutral and earth equipment on 440 3 phase and earth supply safely and if so how?

2 Answers   Maersk,


air condition capacity for masjad having 50feet in circal and 35 feet high

3 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)