Answer / karthik raman.b
its depend on current of the load which connected to the battery amphere per hour if a battery having 10AH it can give 10A load upto a hour
| Is This Answer Correct ? | 9 Yes | 1 No |
Answer / avinash
First you must know the ampere-hour of your battery bank as
per the manufacture's specification.Now discharge the
batteries as per the C5 rating( for Ni-Cd batteries) or C10
rating (for Lead -acid Batteries).Discharging can be done
by connecting the positive and negative terminals of
batteries to the copper plates and immersing in a salt
solution, which will act as a load. The distance between
the plates can be adjusted to set the discharge current.
Measure the amount of discharge current and time till the
battery voltage of each battery in a bank drops to 1 Volt
if it is a 1.4 volt cell. Now multiply the discharge
current and time. This is the measure of the Amperehour
capacity of the bank.If the Amppere -hour capacity as per
the manufacture is available then you can determine the
percentage capacity of your bank at present.Remember that
charging and discharging of battery bank improves the
health of the battery bank.However, for lead -acid
batteries these cycles are around 750 or say 3 years. For
Ni-Cd batteries the life is around 25years or more if
maintained properly.Selecting a overated battery is also
not adviseable as it won't get discharged completely and
this may result in sulfation of batteries and early death
of battery bank.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / sanat ullah khan
Answer
# 1 it depond upon the output load
Thanks for Marking this Answer 0 Krish
Answer
# 2 its depend on current of the load which connected to
the battery amphere per hour if a battery having 10AH it
can give 10A load upto a hour
Thanks for Marking this Answer 0 Karthik Raman.b
Answer
# 3 Hi Krishna,
V HV AN 65AH 32 No's of Batteries connected 60kva UPS,
What will be the full load backup time???
Thanks for Marking this Answer
Answer
# 4 First you must know the ampere-hour of your battery
bank as
per the manufacture's specification.Now discharge the
batteries as per the C5 rating( for Ni-Cd batteries) or C10
rating (for Lead -acid Batteries).Discharging can be done
by connecting the positive and negative terminals of
batteries to the copper plates and immersing in a salt
solution, which will act as a load. The distance between
the plates can be adjusted to set the discharge current.
Measure the amount of discharge current and time till the
battery voltage of each battery in a bank drops to 1 Volt
if it is a 1.4 volt cell. Now multiply the discharge
current and time. This is the measure of the Amperehour
capacity of the bank.If the Amppere -hour capacity as per
the manufacture is available then you can determine the
percentage capacity of your bank at present.Remember that
charging and discharging of battery bank improves the
health of the battery bank.However, for lead -acid
batteries these cycles are around 750 or say 3 years. For
Ni-Cd batteries the life is around 25years or more if
maintained properly.Selecting a overated battery is also
not adviseable as it won't get discharged completely and
this may result in sulfation of batteries and early death
of battery bank.
Thanks for Marking this Answer 0 Avinash
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / mahesh meshram
Calculate the AH of battery as said above or the given by the manufacturer if is same then ok if not then take actual calculated. If capacity of battery is 10AH and load current is of 10A then it will give back up for 1H
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / thowsif_emerson_csm team
Hi Krishna,
V HV AN 65AH 32 No's of Batteries connected 60kva UPS,
What will be the full load backup time???
| Is This Answer Correct ? | 0 Yes | 1 No |
What happen if two protection core (3p) of VT in LAVT are 11kv/root3, 110v/root3 and one protection core (3p) is 11kv/root3, 110v/3
what are the importance of earthing?list different types of earthing.
what is use of starter motor in DG ?
if we appling capacitor at above rated what are looses and what will be happen
4 Answers Radiant, Real Estate,
what is the effect when the shunt field winding is opened in dc shunt motor (i) at the time of starting ? (ii) in running condition ?
what happens if we connect two parallel ideal voltage sources across resistor?what is current flowing through resistor?
From past few months I am getting lagging pf even though sufficient capacitors used in circuit. Where is the problem pls answer
what does the transformer connection symbol YNaod1 mean ?
what is derating factor in Cable ? how we minimise this?
18 Answers Bhel, College School Exams Tests,
what is the formula for 3 phase motor starting cureent deatials 3phase 148A delta 415v, efficiancy 94% can we run the motor with 200A incoming supply
which of the following can produce maximum induced voltage..... (a)1amp dc current (b)50amp dc current (c) 1amp 60 cycle ac current (d)1amp 490 cycle ac current.
tell me any book for current n potential trasformer with full knowledge ?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)