how to calculate the size of cable for 100 kva load,?can
somebody tell me with a formula
Answer Posted / haiat
1KVA=1000VA
1000VA=1000/230A=4.34A
| Is This Answer Correct ? | 9 Yes | 19 No |
Post New Answer View All Answers
what is the value of combined earthing in general electrical circiut?
what is consequences of neutral and earth connect?
why do we need to use 3c+3e cable, normally i select only 3c+e cable and i think it is enough. pls explain the usefull of 3e cable ( in this project the earthing system is well done)
why power factor is important?
What happens to a line-frequency of high-frequency transformer when it is first energized/ re-energize?
what is the voltage between earth & neutral in 3 phase electrical connection.
what is the generator rating for 40 amp load of 3phase motor.?? 400v voltage of generator... plz tell me with formula its urgent...plzzz... and also tell me that this 40 amp at all phases mean 40 amp on red,40 amp on yellow,40 amp on blue...... or the total sum of that 3phase is 40 amp....
advantages and disadvantages of inverse definite minimum time RELAY
Difference between on line capacitor and Station type capacitor
what is the diference between the 4pole & 6pole DC Motors & what is advantage 6pole over the 4pole ?
What is the difference between the relay and the circuit breaker?
Use of switch mode power converter in real-time basis?
working function importance of mdc meter
Why transformer used in UPS??
What is star-delta transformer?