what is anti-pumping relay and the significance of it in a
switcgear cb control system?
Answer / k.prakashchandra
This relay may also be called anti machine-gun relay as it
prevents repeated closing and opening of cb ,while test
charging .If at all you are test charging a feeder after
tripping on fault and the fault still persists, there will
be repeated closing and tripping with control switch in
close- command.This relay will open closing circuit after
the initial closing -command and it allow for next closing
operation only if the closing switch is released
Is This Answer Correct ? | 7 Yes | 0 No |
pls send previous bhel electrical papers
what is the path of electron when a static electron is placed in a magnetic field?
I want to ask a question which i faced during testing of Capacitive Voltage Transformer in AIS. We have measured the C1 , C2 individually , but when we start to measure the total C1+C2 , the testing equipment shuts down and says low loading. Kindly is it possible to find the total capacitance by using measuring device. kindly briefly explain the procedure.
can we use NPT glands in LT panel
Why star delta starter is preferred with induction motor?
Why we are not placing c.B 's btwn generator and transformer.? what happens when generator gets disconnected from transformer when it is running @ full load?
in shunt clippers why a resistor is used in sereis with the input
What is the battery voltage limit
how to test generator protection rotor earth fault relay and locked rotor test?
Does the ferranti effect has some impact on the electricity billing system on high voltage installations?
How can we get d.c series motor characteristics by using a.c induction motor?
HOW CAN WE DECIDE THE SUPPLY VOLTAGE FOR MOTOR ACCORDING TO ITS RATING(IF ANYONE KNOWS GIVE IT WITH EXAMPLE AND ITS CALCULATIONS)