what is anti-pumping relay and the significance of it in a
switcgear cb control system?
Answer / k.prakashchandra
This relay may also be called anti machine-gun relay as it
prevents repeated closing and opening of cb ,while test
charging .If at all you are test charging a feeder after
tripping on fault and the fault still persists, there will
be repeated closing and tripping with control switch in
close- command.This relay will open closing circuit after
the initial closing -command and it allow for next closing
operation only if the closing switch is released
Is This Answer Correct ? | 7 Yes | 0 No |
Three set (each phase contain 2 cable of 400 mmsq CU XLPE AWA) of single core cables are connected to 11 KV motor of 14 MW & the switch gear supplay is taken from 11kv feeder & this supplay taken from 275 KV substation. Problem is one pair cable(L3- 2 cable ) getting very hot & gland melted and damaged in switch gear side. the other two cable haven't any more hot(ambient temp only & L3 haveing 95- 100 Degree C. The same problem happened in 275 KV substation switch gear side also where the supply taken for 11 kv switch gear. But here L2 phese cable had problem. Why it is happening like this?. The cable having temperature different at different location from gland side inthe case of 11KV feeder of 275 kv substation. why ?
Explain cmrr?
who invented electricity?
What does dny11 stand for?
Earth has zero potential then what would be the neutral potential ?
how a.c. genarator control power factor when its conected to grid supply by incrising or decresing excitation voltage.
what are the units of cable insulation?
why use only sf6 circuit breker in 400 kv sub station
Why Delta Star Transformers are used for Lighting Loads.
Define thermal resistance in the context of power amplifier.
why mosquito bat makes noise when it hits with a insect?
What is the difference between AMF panel and DG Synchronization panel? please define the working of both the panels?