Three set (each phase contain 2 cable of 400 mmsq CU XLPE
AWA) of single core cables are connected to 11 KV motor of
14 MW & the switch gear supplay is taken from 11kv feeder &
this supplay taken from 275 KV substation. Problem is one
pair cable(L3- 2 cable ) getting very hot & gland melted
and damaged in switch gear side. the other two cable
haven't any more hot(ambient temp only & L3 haveing 95- 100
Degree C. The same problem happened in 275 KV substation
switch gear side also where the supply taken for 11 kv
switch gear. But here L2 phese cable had problem. Why it is
happening like this?. The cable having temperature
different at different location from gland side inthe case
of 11KV feeder of 275 kv substation. why ?
Answers were Sorted based on User's Feedback
Answer / k.prakashchandra
This happens whenever there is a loose connection or under -
sized lugs are used.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / kaviraj
Get a thermal imager or camera, you will see the loose
connection very easily. I also bet it's a loose connection.
Else one of the cable cores has been broken. Check for sharp
bendings on cable. Copper braids still connected/earthed
properly?
| Is This Answer Correct ? | 0 Yes | 0 No |
which metal is use in shunt
can induction motor run over the rated speed ?
How it can worked plc based electrical system And which type of software using.
if d gen is 50kw,load is 60 kw,hw d gen ll supply d remaining power?
how wecalculate breaking capcity of acb mcb mccb .explain with example
What is fuction of NGT/NGR using in Generator.
why the current leads voltage in the case of a capasitor
how to check a three phase induction motor by multimeter & megger?
kindly tell me how the load on generator increase by just increasing the fuel of prime mover, as if for exampple 20 MW gen set is synchronized the load ramps from zero to 20 MW gradully and during this procress only fuel of prime mover increases. Which thing determines the load on generator with respect to fuel
What is maximum demand and contract demand?
what maximum range of star & delta in hp or kw ?
0 Answers Makkah Hilton Towers,
If two transformers same rating(11KV / 440V)connected in the same primary line(11KV), can we connect(bus coupler) secondary side directly or need a synchronization????
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)