Three set (each phase contain 2 cable of 400 mmsq CU XLPE
AWA) of single core cables are connected to 11 KV motor of
14 MW & the switch gear supplay is taken from 11kv feeder &
this supplay taken from 275 KV substation. Problem is one
pair cable(L3- 2 cable ) getting very hot & gland melted
and damaged in switch gear side. the other two cable
haven't any more hot(ambient temp only & L3 haveing 95- 100
Degree C. The same problem happened in 275 KV substation
switch gear side also where the supply taken for 11 kv
switch gear. But here L2 phese cable had problem. Why it is
happening like this?. The cable having temperature
different at different location from gland side inthe case
of 11KV feeder of 275 kv substation. why ?
Answers were Sorted based on User's Feedback
Answer / k.prakashchandra
This happens whenever there is a loose connection or under -
sized lugs are used.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / kaviraj
Get a thermal imager or camera, you will see the loose
connection very easily. I also bet it's a loose connection.
Else one of the cable cores has been broken. Check for sharp
bendings on cable. Copper braids still connected/earthed
properly?
| Is This Answer Correct ? | 0 Yes | 0 No |
purpose of breaker contact multiplication relay?
If two Transformers are connected in parallel having impedance of 50KA in both transformers will the impedance increase or decrease after connecting transformers in parallel?
Explain (in simple ) - root mean square. whats its role in electrical fundamandal.where its used
1hp= how much rpm
Explain the different methods used in the choice of rotor slots for reduction of harmonic torques in an induction motor.
11 kV line deraction check by an Engineer.
what is the effect if we add capacitor on DG supply, it has any loss or benefit.
Describe the control mechanism of missile launcher???
Baud rate is used to descrice...?
i have done diploma and btech in EE and live in Chandigarh so kindly help me how can i make my competency certificate in my area.
ELECTRICAL ENGINEER TEST IN FEWA ANY ONE HAVE KNOWLEDGE ABOUT THIS?????????
why power factor is only cosine angle not sine angle?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)