Answer / t eswara rao
For lighting loads, neutral conductor is must and hence the
secondary must be star winding. and this lighting load is
always unbalanced in all three phases. To minimize the
current unbalance in the primary we use delta winding in the
primary. So delta / star transformer is used for lighting loads.
| Is This Answer Correct ? | 81 Yes | 5 No |
i think there are mainly two resone
1. in a big sub station or in company power supply is used
for plant load (which is generally use only 3 phase neutral
is not used)this supply also used for plant lighting which
is require neutral to obtain this neutral we use Delta Star
transformer which is also called isolation transformer
2. Delta star transformer is used to isolated secondary
side earth fault (which is common in lighting circuit) from
primary side.
| Is This Answer Correct ? | 7 Yes | 0 No |
Answer / guest
delta-star transformers are used for lighting loads
because in delta side primary side the voltages fed are in
phase (R-Y-B) and thus on the secondary side the star
connection aims at equal currents in all the phases in case
of 3 phase thus equal current flows and thus the lighting
intensity is not disturbed for the lighting loads.
| Is This Answer Correct ? | 23 Yes | 20 No |
Answer / p krishna teja
in delta connection there is no common point ( i:e no
netural) for lighting we need netural line for
maintaining voltage difference. so star connection is need
for lighting .
on delta connection 3 phase we can only get 415 volts as
there is no netural line we cant use individual phase .
But in stare connection 3 phase ther is flexibility of
using individual phases with common netural 230 volts.
| Is This Answer Correct ? | 7 Yes | 5 No |
Answer / b.b.barah nalco
I agree with Mr. P Krishna Teja but one thing is there, to minimize the fault current secondary winding should be star connection and minimize the watt loss.
| Is This Answer Correct ? | 1 Yes | 2 No |
What is the function of mid point voltage in battery bank
1 Answers Jindal Steel and Power,
What is the difference between voltage and emf ?
how to save the power in company?
Wat will happen if R-phase of an alternator is connected to B- Phase of AMF panel fed from alternator
how to control the speed to switched reluctance motor
Please help me regarding my one concern. - During earth pit testing we noticed that the Clean earth pit and dirty earth pit showing continuity (Resistance value - 5ohm) . I want to know that if both earth pit have separate location and there is not internal looping between PIT then why such continuity is showing on it . Because of this issue the field side all earthing point showing short. In PLC panel we are providing two types of earthing cable which is coming from separate earth pit (Clean and Dirty earth pit) because of earth PIT showing short our PLC is not complying spec . please help regarding this issues.
what is difference between vaccum circuit breaker and air circuit breaker?
how to checking earth restence with earthtester
How can we save electrical cost i.e switchgear, wiring, conduiting etc in a room?
sir, iam a electrical engg graduate and i want to go in automation sector and for this i have decided to do industrial training for this,plz suggest me some good institute for the same in delhi,ncr. my degree percentage is 58%, can i get job after doing training, plz help....
what is the principle of singkle phase energy meter?
what type of load we can give to motor shaft?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)