Why Delta Star Transformers are used for Lighting Loads.
Answers were Sorted based on User's Feedback
Answer / t eswara rao
For lighting loads, neutral conductor is must and hence the
secondary must be star winding. and this lighting load is
always unbalanced in all three phases. To minimize the
current unbalance in the primary we use delta winding in the
primary. So delta / star transformer is used for lighting loads.
| Is This Answer Correct ? | 81 Yes | 5 No |
i think there are mainly two resone
1. in a big sub station or in company power supply is used
for plant load (which is generally use only 3 phase neutral
is not used)this supply also used for plant lighting which
is require neutral to obtain this neutral we use Delta Star
transformer which is also called isolation transformer
2. Delta star transformer is used to isolated secondary
side earth fault (which is common in lighting circuit) from
primary side.
| Is This Answer Correct ? | 7 Yes | 0 No |
Answer / guest
delta-star transformers are used for lighting loads
because in delta side primary side the voltages fed are in
phase (R-Y-B) and thus on the secondary side the star
connection aims at equal currents in all the phases in case
of 3 phase thus equal current flows and thus the lighting
intensity is not disturbed for the lighting loads.
| Is This Answer Correct ? | 23 Yes | 20 No |
Answer / p krishna teja
in delta connection there is no common point ( i:e no
netural) for lighting we need netural line for
maintaining voltage difference. so star connection is need
for lighting .
on delta connection 3 phase we can only get 415 volts as
there is no netural line we cant use individual phase .
But in stare connection 3 phase ther is flexibility of
using individual phases with common netural 230 volts.
| Is This Answer Correct ? | 7 Yes | 5 No |
Answer / b.b.barah nalco
I agree with Mr. P Krishna Teja but one thing is there, to minimize the fault current secondary winding should be star connection and minimize the watt loss.
| Is This Answer Correct ? | 1 Yes | 2 No |
What are all the points to be checked while decanting diesel from tanker lorry to HSD YARD
What are two contours of nichols chart?
I want to replace the 3 KW DC motor with AC motor so what should be the rating of AC motor? Details Of DC motor to be changed with AC are - Kw - 3, Vf - 310, If - 0.15, Va - 400, Ia - 13, RPM - 2400
What is the formula for calculating Transformer Losses & Efficiency. I want to compare the Transformer efficiency at different loading condition.
6 Answers Rays Power Experts, Techser,
shall we use a machine having 60Hz frequency in india ? why?
We are getting supply at33kvand it stepdown to 11kv.So Our requirement is 11kv voltage.why we draw 33kv from the grid instead of 11kv?
In our factory so many iron pillors are exists for supporting the shed/Hangar. If do more no of earthings at one piller instead of doing more earth pits in many locations and running earth strip around the hanger, I can save the money. Please suggest this method is acceptable as per Is specifications though the Earth resitance of the farthest piller is with in the limits as per IS specifications.
125Kva Dg can take up how much amphere load.
What is difference between potiential,volatge and emf
why usa use 60hz and 110v?
what is the procedure for three phase motor differential relay testing can it do with single phase test kit?
How does numerical relay work?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)