explain me how a power factor is improved by adding a
capacitor?what capacitor do to improve it?in simple words
and in detail?thx
Answers were Sorted based on User's Feedback
Answer / amit upadhyay dscl
because
cos$ = R/Z ........... ($=phai),
where R=resistance & Z=impedance
total impedance without capacitor,
Z=root square of(R square + XL square)
total impedance with capacitor,
Z=root square of{R square + (XL-XC) square}
due to decrease of (XL-XC) total impedance with capacitor
decreases, and due to this, power factor increases. because
from equation first,
cos$ perportional to 1/Z
| Is This Answer Correct ? | 8 Yes | 1 No |
Answer / bala
current leads the voltage by 90 degree by adding the
capacitor bank. this helping to increase the power factor.
| Is This Answer Correct ? | 6 Yes | 1 No |
Answer / amirtha
in capacior we having leading power factor.so it is used to
improve power factor.
| Is This Answer Correct ? | 8 Yes | 5 No |
Answer / mohan
An electrical load can be inductive or resistive(filament
bulb).
for an inductive load the energization power is required ,
isnce this is called reactive power(imaginary magantising
power) , which is non productive.
You can draw paralles to your Savings Bank account - where
you need to maintain certain amount as minimum balance,
which you can not withdraw.
again this "magnatising current" is load dependant and will
varry according to the load. for example if you are riding
a bicycle , the minimum force needed to be given for moving
the cycle must be higher than than Weights(your+Cycle)
*gravitation force.
The base value weight* gravitational force can be imagined
as reactive power and, when you ride the cycle in elevated
path u put extra energy and on a slope u need less energy.
Capacitor is a supplier of reactive energy and if you use
capacitor to compliment the reactive power then you will
have reduced kva withdrawal from grid.
KVA = SQRT[kw*kw)+(kvar*kvar)]
PF = kw/kva. in other words PF is the efficincy of yor
power conversion. since it is the ratio of output(KW you
consume ) to the input(the withdrawal from grid)
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / viswanathan
we are using induction motors for industrial and domestic
purpose.inductions motors working with reactive power.it
leads to lagging power factor.so we put the capacitor
(active power)for compensat the reactive power.
| Is This Answer Correct ? | 4 Yes | 3 No |
Answer / p.muralikrishna
My dear friend,
I think you are aware of mechanical fly wheel. This sores
energy when there is excess of supply and supplies the
stored energy when there is short to the extent of its
storing capacity. Also as the capacitor draws a leading
current in contrast to generally lagging current by
inductive load. Thus capacitor tries to bring the load
current nearer to resistive.
| Is This Answer Correct ? | 2 Yes | 1 No |
My dear friend,
I m describing the answer very simply. If the load is
inductive load i.e. 100 Amp motor load. Then some current
i.e. 75% (75 A) will be drawn by Electricity line & balance
25% (25 A) will be drawn by Capacitors if they are connected
before load. so Electricity billing reduced only for 75 Amp
instead of 100 Amp.
I m using same system for transformer testing. So
technically we can say that we improve PF by using
capacitors, so that we get benifit in Electricity Billing.
If you want further clarification, plz write me on
ashish_patel111@yahoo.com
| Is This Answer Correct ? | 1 Yes | 5 No |
what is the acceptable insulation resistance for motor/transformer?
2 Answers Reliance, Tata Motors,
i am using star-delta connections with reverse/forward direction motion of the 75hp induction motor.What should be the ratings of Main,Delta and Star contactors and why?
what is the difference between synchoronous and alternator and induction motor and generator
what is frequancy
What is Autodialer used in FAS????
What is the formula formula for Busbar sizing and what are the things to be consider for Busbar Calculation?
what type of relay has to be used for tripping the circuit from mains when a fault occur in a machine
CONSIDER A 415V/200V STEP DOWN TRANSFORMER.CAN WE USE USE IT AS STEP UP TRANSFORMER BY GIVING 200V IN SECONDARY AND TAKING OUTPUT FROM PRIMARY?
if 400kv line is connected to the load but neutral ii not be connceted then wt ll happen
how can service sitting be setted for MCCB?Example for sittings IR (CURRENT RATING),IS(CURRENT STARTING)IO (current operating)?
The cable area of cross section is 185 sq mm. How to convert this to the diameter.
diagram for soft stater ?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)