i am using star-delta connections with reverse/forward
direction motion of the 75hp induction motor.What should be
the ratings of Main,Delta and Star contactors and why?
Answer / jakeer
well you are using 75 HP(55KW) motor.its flc is 96amps at 433 volts.
1.Main contactor:200amps rating.
2.Delta:200amps.
3.star; 125amps.
Is This Answer Correct ? | 7 Yes | 0 No |
Why we Do not connect the windings of the motor in delta? & what would happen if we do that? I mean the winding themselves not the three lines that are coming to the motor?
what is real and reactive power?
What is DPR relay, And what for??
how to identify the cable quality and what is flame proof cable
How much current can a 3-1/2 core 100 mm wire carry?
3 Answers Epitome, Focus, Focus Energy,
Why Lightning arrester used? Can we use piece of iron as a core material of transformer, if No, why? In CRGOSS material what is meaning of cold rolled grain oriented? Why Impegrenation of Transformer is done? Properties of Insulator? what is phase angle? Testing of transformers (Routine & Monthly)?
HOW WE CAN REDUCE THE CIRCUIT COMPLEX OF STAR-DELTA STARTER .BECAUSE NOW WE USING ONE TIMER RELAY & THREE CONTACTOR FOR MAIN,STAR & DELTA ?IF ANY IDEAS PLZ POST.THANK U
what is tertiary winding in transformer?What is its purpose?
If we have two nodes A and B and Vab is the potential difference between these nodes then which node is called reference node a.node A b.node B c. Ground node
how to calculate fault level?
lorteny method
why anti pumping relay is not given to tripping coil of the breaker? why only to closing coil?