i am using star-delta connections with reverse/forward
direction motion of the 75hp induction motor.What should be
the ratings of Main,Delta and Star contactors and why?
Answer / jakeer
well you are using 75 HP(55KW) motor.its flc is 96amps at 433 volts.
1.Main contactor:200amps rating.
2.Delta:200amps.
3.star; 125amps.
| Is This Answer Correct ? | 7 Yes | 0 No |
Why neutral point is consider as zero potential?
what are the effects when a salient pole alternator is run at high speed like 3000 r.p.m?
Uses of induction motor
what is high tension ? specify the range?
How many percent of power are not being registered if we bypass one side of the meter base terminal using #8 cu wire on 1-phase kwhr meter.
Why we are designed only 11Kv and 6.6Kv Alternators, not 33Kv Alternators and Power Transmission side we are designed only 220kv, 120kv, 66kv, 33kv, 11kv, and 440volts, not 20kv, 50kv, 100kv.
how to create new innovation what are the supporting sources in the electrical field for Electrical engineers.....?
Why L.T.Cable voltage rating is 1.1kV,where as system voltage is 0.415kV?
which strater used genearalyy???and why???
why in generating station generation voltage is 11 kv
what is diff. between earthing grid,earthing mess, earting grid?
0 Answers Century Rayon, Emco, Tailor Solution,
transformer 3 ph, 225 kva pri 480v, sec 208v. primary neutral connected to system, is secondary neutral to be grounded and how
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)