what is the acceptable insulation resistance for motor/transformer?
Answers were Sorted based on User's Feedback
A very significant maintenance procedure for checking out the working condition of an electrical system is called IR test or Insulation resistance. It can be said that ht system or equipment is fine when insulation resistance is high.
Megger is an insulation resistance measurement tools for finding the equipment’s insulation resistance. Let us see how is the IR calculated? for more : http://crbtech.in/Electrical-Training/index.php/2017/07/31/define-insulation-resistance-and-its-calculation/
Define Insulation resistance
There is an application of direct current (DC) and not alternating current (AC) and this is the first thing while doing the Insulation resistance test.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / gajendra singh
Insulation resistance tests are made to determine insulation resistance from individual windings to ground or between individual windings. Insulation resistance tests are commonly measured directly in megohms or may be calculated from measurements of applied voltage and leakage current.
| Is This Answer Correct ? | 2 Yes | 3 No |
How to select the proper VSD to operate high inertial load
What is a Phase shift meter? Where can I get one?
What is the de rating factor of cable? What is the importance of the de rating factor in cable selection?
what is power load and lighiting load?
what is electrical machines
If Polarization index of motor 8.75 at 500volts of medium voltage 4.16 KV motor what this mean winding good or bad pl answer if any reffrence book give me the link
what is the calculation involved to design the heater to heat 10KL of water in temperature control unit?
What is the unit of inertia constant of rotating machines? Which has more inertia constant between turboalternator and hydroaltermanor and why?
If I want to use capacitor banks at HT (11 KV) side for maintaining power factor then which type of capacitor should I use? Plz give me the specification?? (I am using 1250 Kva transformer (11 KV/433V)).
What is the distance b/w R&Y phase in 33kv T.line,11kv &440v
Which type of losses in transmission Line
A Generator is in running condition and Rotor earth fault alarm is coming.How to check on line(i.e in running condition) whether there is actual earth fault in rotor or not.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)