What are the Safety measures in central chiller plant?
Explain them?
Answers were Sorted based on User's Feedback
Answer / sudeep
1)Refrigerent Discharge pressure high
(2)Refrigerent Discharge temp. high
(3)Condensar water flow fail.
(4)Chiller water flow fail.
(5)Oil Discharge pressure low.
(6)Compressure motor trip. low & high voltage..
(7)Antifreeze
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / de3epak
1.High presser
2.Low pressure
3.Oil pressure
4.Anti Freezer
5.Water Flow Switch
6.Pressure relief valve
Is This Answer Correct ? 0 Yes 0 No submit
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / anand kumar singh
(1)- Evprotor low temp.
(2)- condesor high temp.
(3)- low pressure.
(4)- high pressure.
(5)- Refrigerant level
(6)- oil level.
(7)- Flow switch
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / sunil kumar
1.High presser
2.Low pressure
3.Oil pressure
4.Anti Freezer
5.Water Flow Switch
6.Pressure relief valve
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / deepak kumar
high pressure low pressure cutout
# high tem. Low tem. Cutout
# pressure release valve
# Solenoide valve
# Expansion valve
# flow switch
| Is This Answer Correct ? | 2 Yes | 0 No |
High pressure controller switch.
Low pressure controller switch.
Low oil pressure.
Anti freeze.
Water flow switch.
Fusial plug.
Pressure relief valve
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / faisal
High pressure
Low pressure
Balancing valve
Motorise valve
Oil temperature
Aqumelater
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / jaheer hussain
hp,lp,oil pressure regulator switch,antifreez thermostate,waterflow switch,voltage monitor
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / manish yadav
High pressure (head pressure)
Low pressure
Water flow switch
Anti frezier
Oil pressure
Over load relay
| Is This Answer Correct ? | 1 Yes | 0 No |
what is meant by LT & HT?
what is meant by the phrase 'static load' in case of shorting in a generator excitation system?
Are Refrigerators & Deep Freezers the Inductive load ? How to calculate the Power Factor & hence the Output Power for them ?
How to connect frequency meter in metering circuit?(single phase and three phase frequency meter)phase to phase or phase to neutral
List the characteristics of filter?
our plant maximum demand has 500 kva.need to suggest me to maintained pf 0.98.how much capacitor bank will be connect to the supply line.
Why use prefer Dc drive in place of Ac drive for kiln Operatio in Cement Plant?
What is MSL designation of a motor and same may be provided in details.
why normally Generator rating are between 11Kv to 22Kv?
How would you supply power to a village which is very far from a sub-station and has only a 11kV line running near by?
For a 50MVA (138/69/13.8 KV) transformer, what would be the maximum demand in order not to exceed 80% of its operating capacity.
how the 6.6KV motor can be used with 11KV?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)