Answer / madhusudhan
Kw= 1.732X Voltage X Current X pf. in these parameters only
current and pf are variable. The current limitation given on
the DG set is at that pf. if pf increases the current will
get decreased for the same KW. so you should monitor the
same pf as mentioned of DG set name plate or else you should
reverse calculate the current limitation at your load pf and
monitor the DG set no to get overloaded.
| Is This Answer Correct ? | 5 Yes | 2 No |
I try this,
see,power factor is the percentage of resistive load in the
total circuit.as the power factor is one it indicates the
pure resistive which is real in number which can be
converted to the what ever the real energy we want like
rotatory motion etc...
frm:rajeshbeesetty@yahoo.com
| Is This Answer Correct ? | 3 Yes | 1 No |
Answer / balajieee
power factor is the cos angle between voltage¤t.using
that nameplate pf value u can find kw capacity of a
generator for its kva rating(formula,p=sqrt3*v*i*cospi.).if
you are connecting pure resistive load means power factor
is unity,so the pf of generator will incrase from its name
plate value.capacitive load also incrase the pf of
generator.inductive load will decrease pf value.so the
average of resistive,inductive,capacitiveload pf ,name
plate pf will give final output pf of generator.
| Is This Answer Correct ? | 3 Yes | 13 No |
What is 100% protection of generator? Why 95% protection is used not 100%?
how many types of ACB breakers, describe briefly..?
block diagram of 2 ups system connected in hot stand by mode?
whether inrush current for lamps or capcitors should be considered cable sizing to feed that load.
which electrical supply used for long distance traction 1.1-ph 22kv a.c 50hz 2.2-ph 22kv a.c 50 hz 3.dc vtg 4.1-ph 22kv 150 jhz
what is a bus post insulator? explain its application in a substation.
we the the value of frequency is 50 HZ in DG then why we said the value inductive rectance is zero in DG?
Why the underground cables will Punchar? or what is the reason to burst the underground cables?
What is mean by retrofitting of machine tool please brief.
what is the value will come when megger the phase to phase ,phase to neutral ,phasae to ground ?
why transformer comes only in standard rating like 11kv,33kv,66kv....and not like 33.33kv and so on?
What happens if the negative to earth voltage is greater than positive to earth voltage in the battery of substation?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)