In the diesel generator if there is an AVR (auto voltage
regulator) gone faulty, in this condition is there any way
to generate the voltage from the alternator? I need a brief
explanation can you please help somebody
Answer / sheikh
in any type of generators if AVR has become failed
then not possible to generate the voltage, because excitation
is comulsory to megnetized the alternator field winding
in case of AVR faliuer exitation also must be failed becaus
AVR is supplied the exitation volage either no load condition
or on load condition AVR also incrase and decrease the
exitation voltage and current as per demand of load.
Is This Answer Correct ? | 5 Yes | 0 No |
what is role of mpu in dg
How much load can take a 16 mm aluminum cable 3 phase
What is fault level? How can be calculate the fault level?
sir please tell 1 ton equal to how many kilo watt?? in some converter software's that is 3.5 kw. is it right?
Is a direct shorth ciruit on a branch MCCB in a Low Voltage Switchboard a correct means of tesing the performance for discrimination?
Define cuttoff frequency?
In electrical cables what is U and U0 refers?
Application Comparison between 22KV (UE)and 33KV (E) system. Are we allowed to use 33KV (E) cable in lieu of 22KV (UE) cable. What are the technical disadvantages.
what's the activities of reactor in Buchholz relay?
what is the requirement regarding earthing of Single conductor with AWA
What core magnetic balance test of transformer? How to do this test in a three phase Star star (star-LV, star-HV) transformer? How to measure and where to measure?
how we calculate the dick for a pole?