how to select short circuit current while selecting a MCCB?
how to calculate current for a given KVA and KW load?
Answers were Sorted based on User's Feedback
Answer / john
FOR A 1000KVA TRANSFORMER.
PRIMARY VOLTAGE=15000V=15KV
SECONDARY VOLTAGE=480V=.48KV
impedence =5.75%
short circuit current at primary=1000/15*1.73*.0575=670amps.
short circuit current at
secondary=1000/.48*1.73*.0575=20943amps.
Is This Answer Correct ? | 30 Yes | 8 No |
Answer / prashant
The basic equation is
P= 1.732VICos(A) WHERE P = load in KW
If in KVA then convert it to KW
KW = KVA * Cos(A)
V=415
well i dnt knw regarding the short ckt selection of MCCB
Is This Answer Correct ? | 2 Yes | 13 No |
we can run 2phase as 3phase .what will be the differnce with respect to phase angle, power, current between the two modes
what is droop?
why we do not switched on capicitor panel with DG Supply
a)In a 3-phase 4-wire circuit, a circuit breaker is selected to protect the circuit whose highest fault level is 6.6 MVA. Determine the required minimum breaking capacity in kA. (Note: Covert 3-phase power in terms of kA to find answer.) b)Using the below, determine the required minimum making capacity in kA as a “peak value”. Rate breaking capacity (Icn) ka: Icn<= 1.5 Factor = 1.41 1.5
What is principal to reduce earth leakage current with isolation transformer? When isolation transformer is installed in input stage of system, earth leakage current is reduced. the reason is why the leakage current of 2nd stage of isolation transformer does not affect the 1st stage's leakage current. I would like to know the reason. As you know, earth leakage current is a kind of AC. So, How to reduce earth leakage current in case that isolation transformer is used?
what is the lightning arrester rating for 3.3kv system voltage
Is necessary Protection CT, CLASS - 5P10 fitted at Incomer side of main Breaker ? Why ?
HOW TO CALCULATE EARTHING SIZING?
Which type of transformer is used for lighting loads?
How can decide the MVA rating of power transformer for substation like 220/132, 132/66, 66/33kv etc or even higher kv rating of substation???? Send me the strictly technical answer that shows your strong technical aptitude.
Pls Breifly explain about UPS (Inverter,Reserve,Rectifier,Float voltage,Boost voltage).
how can findout cable fault Location only useing MEGGER