how to select short circuit current while selecting a MCCB?
how to calculate current for a given KVA and KW load?
Answers were Sorted based on User's Feedback
Answer / john
FOR A 1000KVA TRANSFORMER.
PRIMARY VOLTAGE=15000V=15KV
SECONDARY VOLTAGE=480V=.48KV
impedence =5.75%
short circuit current at primary=1000/15*1.73*.0575=670amps.
short circuit current at
secondary=1000/.48*1.73*.0575=20943amps.
Is This Answer Correct ? | 30 Yes | 8 No |
Answer / prashant
The basic equation is
P= 1.732VICos(A) WHERE P = load in KW
If in KVA then convert it to KW
KW = KVA * Cos(A)
V=415
well i dnt knw regarding the short ckt selection of MCCB
Is This Answer Correct ? | 2 Yes | 13 No |
A well system is when , no. of bus bar is less or more. Tell me the concept of it.
how we sesign the transformer give some specifion regarding design of transformers
can we use 400w coke instead of 250w choke in 250w fittings
if field winding of synchronous generator are shorted on each other will it start or burn or run for short time like induction motor
suppose generator rating is 50 kw,load is 25 kw,hw much d generator ll generate?what about d remainin power?
what are the difference between protection class CT and Class PS CT
what is rated speed?
DEAR SIR, HOW TO CALCULATE WELDING TRANSFORMER CAPACITY IN KW OR KVA (POWER). TWO WELDING TRANSFORMER USED WHAT TYPE OF DG SET CAPACITY LIKE ( 45 KVA OR 62.5 KVA), PLEASE TELL THE WELDING TRANSFORMER RATEINGS. I AM REFINARY (TANKS WELDING) THANKING YOU
What is the drawback of class b amplifier?
How is the AVR working?
2. A current i=(10+10 sin t)amperes is passed through MI type ammeter. its reading will be.........
control & auxilary circuits used for circuir breakers