why we do not switched on capicitor panel with DG Supply
Answers were Sorted based on User's Feedback
Answer / hitesh
when Dg set is on, reactive power needed in system is
controlled by the avr system.
when we connect external capaitors then the system will run
on leading power factor hence also reducing active power
supply of alternator.
Is This Answer Correct ? | 5 Yes | 2 No |
Answer / arvind kumar
DG sets are used to supply local loads and as per designing
of DG the power factor is consider 0.8, hence in this case
capacitor bank may not required.
Is This Answer Correct ? | 2 Yes | 1 No |
Answer / i.m.sayad.
In an AC circuit capacitors are used to improve PF,and in
single phase motor for phase displacement,it charges and
discharges continuously till it is connected in the line,so
it draw some current.DG are designed for certain load,it
generate desired load current.If AC Capacitors connects in
DG supply,DG could not fulfill your connected load
requirement.
Is This Answer Correct ? | 0 Yes | 0 No |
What is fault level?How it is calculated and how it is Expressed?
wht is an AVO metre. and whre it is used?
what happens when the supply frequency to the tube light is reduced to 25Hz....?
what is the preventive maintence for ht panels and busbars and vcb abd acb's.
what is ATS & RING MAIN UNIT in Distribution System?And its Function.
How out of step protection relay works?
what is power factor in ac ckt ?
Why Neutral Busbar CT & transformer neutral CT connected with phase CT in Restricted Earth Fault?
simple way to find busbar sizes??
how you can select circuit breaker for 2000kva transformer?
Master trip relay code no
whay we transmit power in 3phase no in 4 or 2 or 5......etc?