How can decide the MVA rating of power transformer for
substation like 220/132, 132/66, 66/33kv etc or even higher
kv rating of substation????
Send me the strictly technical answer that shows your strong
technical aptitude.
Answers were Sorted based on User's Feedback
MVa Rating is Depends upon the Load when Load is
increased current will increase so we design for different
rates of Mva Depends upon the load
S= 1.732* V*I for Ex 50 MVA
50* 10^6 = 1.732* 220* 10 ^3*I To Calculate the I Value
is 131 in Hv side Lv side 218 A
| Is This Answer Correct ? | 23 Yes | 4 No |
The MVA rating is only based upon the generating MW capacity
of the plant.
For Example:
50MW is generated in the Powerplant.(i.e. Generator
capacity is:50MW,11kV,0.8P.F,3000RPM)
Now we like to connect this 50MW power to the E.B.grid
then we use one Step UP Transformer i.e. to step up the
voltage from 11kV to 220kV.
Now we can calculate the MVA rating of that step up
transformer as:
i) MVA = MW/costeta
MVA = 50/0.8 = 62.5MVA.
This is the answer.....
By,
Karthik(Engineer)
| Is This Answer Correct ? | 11 Yes | 7 No |
Answer / srikanth.kondru
very simple
we need to know the Load of the sub station ..
for example it is 1000 H.P
as we know that 1 H.P =1.5 amps
voltage is 220 KV
power ,p = 746KW = 1.732*0.8*220KV*I
I = 746 KW/1.732*0.8*220KV
= 2.4 amps
S=220*2.4*10^6 =532 MVA
| Is This Answer Correct ? | 5 Yes | 3 No |
Answer / milinda4p
The MVA rating of a power transformer depends on the load
connected to the transformers. this can be calculated (for a
grid transformer) by calculating the total MVA of the
primary substation transformers connected to it.Generally
this is calculated with a extra space for load connection.
| Is This Answer Correct ? | 4 Yes | 2 No |
Answer / k.prakashchandra
The present load and anticipated load growth in the coming
10 years.
| Is This Answer Correct ? | 3 Yes | 3 No |
Answer / raju
transformer is working only based on load. frequency was not changing, so it is called mva
| Is This Answer Correct ? | 2 Yes | 6 No |
an ac induction motor gets overheated when operated at a low frequency of 25 hz a instead of 50 hz. reason?
What happens to a line-frequency of high-frequency transformer when it is first energized/ re-energize?
is it possible to have dc motors on single chip
We have a 12MW power plant & we inject 5-6MW power to Orissa GRID. For this we have a 33KV/11KV switch yard having 12.5MVA power transformer. Some times we draw power during emergency. It is observed that during Export or Import for load less than 500Kw the power factor is decreasing to 0.3 . This is happening only during export or import. During island condition TG power factor OK.Our capacitor bank is provided with our Power plant auxilliary load. Please suggest how I can we improve our power factor during low load (GRID).
What are the protection used for alternator,transformers.
which type of capacitors using in single phase motors
why h parameter are called as hybrid parameter?
volts=230 c=10mf a=??
To attain a powerfactor more than .95, how much kvr should we use for 100 HP of current
4 Answers Bhel, Scooters India,
i have to use generator in my project,which gen. i can use?
Why we are using only Dyn11 tranformer in distribution system but not using a Dyn1 in distributing system?why not and advantage and disadvantage in both
What is the difference between online and offline UPS
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)