how to select cable size?
Answers were Sorted based on User's Feedback
Answer / brewed
There are many factors to consider when choosing cable
size .nd I will list just but a few.
1. You need to know the kind of load.
2. you need to know if its undergrond, overhead, in or out
doors
3. You need to know the temperature of your environment.
4. You need to consider the atmospheric pressure
With these and other facors you multiply them, depending on
your installation rules, to get a k factor which will then
depend on rated current carrying capacity of the cable at
hand.
| Is This Answer Correct ? | 13 Yes | 4 No |
1.Voltage level.
2.Type of cable going to used.
3.Whether the cable is going to laid in air,tray or in
burried.
4.Derating factor, Grouping Factor and ambient temperature.
5.Voltage drop as per the standards.
| Is This Answer Correct ? | 5 Yes | 3 No |
Answer / fida
I am using transformer turn ratio tester for 250KVA 13.8KV
primary and 220V secondary transformer what should be the
correct values of turn ratio test how i assume the correct
values for turn ratio.
| Is This Answer Correct ? | 3 Yes | 6 No |
Answer / leturtle
It is normal practice to have a rating for the earthing
system commensurate with the maximum system design fault
level. The normal maximum 400kV fault level is 63kA 1s.
Take the formula from EA TS 41-24 [6]
If you can't find it go to www.ees-group.co.uk on the FAQ
section.
| Is This Answer Correct ? | 1 Yes | 4 No |
Dear sir, In our plant have Station Transformer having capacity,i want to know, why LV side 40 - 40MVA is given? & how we can get 6.3 KV supply from tertiary(i.e. Open delta connection), Vector Group YNyn0 - yn0 +d MVA Rating 80MVA / 40 - 40MVA + 26.7MVA Voltage rating 420 (Tap range +6,to -10)81.25% /11.5KV - 11.5KV +6.3KV
how to reverse the direction of universal motor?
what is relation betn. KW & KV?
Whata are the types of Cables?
why the measure taken in multiplication factor of 11for voltage like.. 110V,220V,440V,1.1KV,6.6KV,11KV,33KV,66KV,110KV,132KV,220KV
Hi I'm doing my MBA(3rd semester).I applied for the post of ET conducted by BHEL the last year.I cleared the written and lost in personal interview.Again I wrote the exam this time and cleared the written n yet to take the personal interview.Shall I disclose in the interview about my studies.What shall i say if they ask about my change from studies to job
I have 1 KW, 3ph. 440v, 50 hz, cos(phi) .75, efficiency 75%(star delta connection)Motor. How to calculate line current & Phase current (1) Star connection (2) delta Connection
what will be the magnetizing current in the testing of 27 MVA transformer?
HOW TO CALCULATE EARTHING SIZING?
Hi,Any one has idea regarding the KPTCL Recuirtments for AE'e & JE's for the year of 2009-10???Kindly help in regards..
What is the formula that shows relationship between voltage and speed in an induction motor
i Have 1000kva 11/.4 kv voltemp make t/f Its a 2 year old. i wants to known how much iron losses & copper loses during no load condition.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)