how to calculate the multiplication factor in HT incomer
trivector meters
Answers were Sorted based on User's Feedback
Answer / sunil kumar das
MF=PT Ratio x CT Ratio
Ex: PT ratio= 33KV/110V
CT ratio= 40/1A
so please this value in formula
MF: 33KV/110V x 40/1A = 12000
| Is This Answer Correct ? | 119 Yes | 46 No |
To calculate MF(multiplication factor) we must know current
transformer ratio and meter ct ratio
mf = current transformer ratio/meter ct ratio
| Is This Answer Correct ? | 75 Yes | 34 No |
Answer / mohamed ali.m
Hi,
this Correct Ans,
MC = PT Ratio x CT Ratio x Dial Constant/ Meter PT Ratio x
CT Ratio
For Exmple : 100x60x1/1x1 = 6000( This MF)
| Is This Answer Correct ? | 30 Yes | 20 No |
Answer / ripun
Mf=field ct ratio/meter ct ratio *field pt ratio/meter pt ratio
Let field ct ratio=15/5a
Field pt ratio=11kv/110v
Meter ct ratio=-/5a
Meter pt ratio=-/110v
M.F=15/5*1100/110=300
| Is This Answer Correct ? | 21 Yes | 15 No |
Answer / chandu
multiplication factor is depending upon CT Ratio Thats o.k
but if meter constant is given what will be the
multiplication factor for 600/5 CT
| Is This Answer Correct ? | 8 Yes | 4 No |
Answer / er l r daroch
Line ctr 50/1a
Meter ctr 50/5a
Is it a right combination
| Is This Answer Correct ? | 4 Yes | 5 No |
Answer / sureshmuthusamy
MF = External ct ratio*external pt ratio/metering ct ratio* metering pt ratio(if there)
= 40* (110000/110)/1*1
= 40*1000
=40000kw
= 40w(40000/1000)
so,MF is 40(your daily tariff meter consumption (kwh)*40= consumption /day.
| Is This Answer Correct ? | 1 Yes | 3 No |
Answer / rajesh sutar
MF= CONNECTED CT/METER CT *CONNECTED PT RATIO/METER PT ratio
*space factor
(space factor =1)
| Is This Answer Correct ? | 5 Yes | 12 No |
Will sag depends on the Specific Resistance of the conductor?if not Why??????????
Between rotating armature type and rotating field type arrangements which one is adopted for large rated alternators and DC generators.Why there is difference in the choice?
The loads are connected with phase and ground then why current flow as the loads ?
How to calculate cable size in sq units based on motor rating is KW
wwht is wave trap used in ht line
How to calculate the diesel generator efficiency? what details are required to identify the running diesel generator sets with 1000 kVA & 180 kVA?
11 Answers Greeves, Sudhir Power,
We know that, in case if there is a faulty insulation,or sc, the current is bypassed to earth through the earth wire that has low resistance.Actually, what will happen to that current that flows through gnd?In that case,if we come in contact with that faulty appliance, wont that current flow through us as we form a closed path by standing in gnd?Is grounding a safety measure?
what is hormonics. how it is generated & what are the problem faced by that.
how we select the mva rating of the circuit breakers?
Why is voltage is required to be within permissible range for an electrical equipment?
Why converter duty transformer neutrals are not earthed...i am still not sure if this question is also correct...Please email at ranjan120482@gmail.com
if grounding is notdone at regular intervals for long distance transmission, will the load connected at distribution end receive voltage during negativehalf cycle of the sine wave?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)