what happens when d cexcitation given to alternator is
removed while it is running or what happens when dc
excitation is failed in alternator while running?
Answers were Sorted based on User's Feedback
in this case alternator wil work as induction generator, as
reactive power supplied by AVR wil be zero due to loss of
excitation, generator wil be in asynchronous mode.
Is This Answer Correct ? | 48 Yes | 9 No |
when excitation is lost due to fault or field breaker
tripping . Reactive power will be supplied by the system and
generator will work as induction generator and its speed
will rise a little . generator which was in over excitation
mode will work in underexcitation .
but there is under excitation limit which should not be
reached so we should detect loss of excitation and trip
generator
Is This Answer Correct ? | 11 Yes | 4 No |
Answer / sunil kumar
when the excitation is lost,alternator tends to behave as
induction generator because there is no opposition to the
rotor as flux is zero, rotor speed tends to increase beyond
synchronous speed and by reactive power from the grid the
machine behaves as induction generator as slip is negative
and reverse power flows which will be taken care by
directional relay.
Is This Answer Correct ? | 7 Yes | 3 No |
Answer / nishad
Generator will not produce any output voltage and it will trip the generator output breaker by the loss of excitation monitor protection relay or under voltage relay. If the breaker not trips by these relay, it will trip by reverse power relay. Due to the presents of Reverse Power relay, it will not allow the Generator to run as an induction generator and will trip the Generator breaker, thus it protect the generator from further severe fault. Again, if it not trips by these all protections, alternator will work as induction generator due to the residual magnetism in the field core when it is running in parallel and it will give the over load to another generator as a result, it will trip entire system. Also, as an alternator typically isn't designed to operate as an induction machine, the windings on these machines will heat up and damage. Therefore, need to make sure the reliability of protection relays to avoid such faults.
Is This Answer Correct ? | 3 Yes | 0 No |
Answer / atul
if excitation fails let d case of hydro generator the prime
mover is turbine. since turbine ic moving and is coupled
with generator shaft and no flux to control its speed it
will go out of path or speed will increase beyond
synchronism
Is This Answer Correct ? | 8 Yes | 6 No |
Answer / ramlakhan y adav (ballia)
when the excitation is removed then the alternator work as a
asynchronous motor will draw the power from reverse supply.
Is This Answer Correct ? | 7 Yes | 5 No |
Answer / manjeet
duction generator as underexcitation .
but there is under excitation limit which should slip is
negative
and reverse power flows which will be taken care by
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / raj
Every one is right but one more thing will happen that is
Alternator will work like motor and will draw power from
other source ( with that it synchronised )known as reverse
power and further RPR will trip the Alternator breaker.
(Approx continuous rating for reverse/negative power is 10%)
Is This Answer Correct ? | 7 Yes | 14 No |
Answer / vijin
if the excitation fails the motor will simply stops,because
it loses the magnetic locking capability by the removal of
dc supply. the motor has no field suplly to generate
necessary emf while running by virtue of the inertia.
Is This Answer Correct ? | 3 Yes | 14 No |
HOW TO TEST A LIGHTENING ARREST ER ?
0 Answers Bhushan Power Steel,
What is the slip speed?
What is the minimum value of hfe for the oscillations in transistorized rc phase shift oscillator?
What is the operating range(tolerance) of voltage and frequency of grid supply in india?
what is difference between fuse and circuit breaker?
What are the Safety measures in central chiller plant? Explain them?
22 Answers Carrier, CPIC, HSL, JLL,
help!!!! i bought a new house 2 yrs ago,ive just had 2 new lights fitted,when i boil the kettle,maybe 2 times in succession the safety light switch trips out,it dosnt do it straight away but it seems to do it when the kettle boils!!!!! sounds very odd to me
Earth Is a very good conductor or very good insulator.? If a good conductor then why current donot flow through small piece f earth and if a good insulator then why we use it as return path in lines.???
Send the control circuit digram of a star delta stater?
What the purpose of transient fault recoredr in substation
what would u consider to be the basic purchase order information you would need to proceed with a cable inspection assignment?
i karmveer bharti persuing b.tech . plz send me syllabus and name of reference books. for preparation of section eng.