what happens when d cexcitation given to alternator is
removed while it is running or what happens when dc
excitation is failed in alternator while running?
Answers were Sorted based on User's Feedback
in this case alternator wil work as induction generator, as
reactive power supplied by AVR wil be zero due to loss of
excitation, generator wil be in asynchronous mode.
| Is This Answer Correct ? | 48 Yes | 9 No |
when excitation is lost due to fault or field breaker
tripping . Reactive power will be supplied by the system and
generator will work as induction generator and its speed
will rise a little . generator which was in over excitation
mode will work in underexcitation .
but there is under excitation limit which should not be
reached so we should detect loss of excitation and trip
generator
| Is This Answer Correct ? | 11 Yes | 4 No |
Answer / sunil kumar
when the excitation is lost,alternator tends to behave as
induction generator because there is no opposition to the
rotor as flux is zero, rotor speed tends to increase beyond
synchronous speed and by reactive power from the grid the
machine behaves as induction generator as slip is negative
and reverse power flows which will be taken care by
directional relay.
| Is This Answer Correct ? | 7 Yes | 3 No |
Answer / nishad
Generator will not produce any output voltage and it will trip the generator output breaker by the loss of excitation monitor protection relay or under voltage relay. If the breaker not trips by these relay, it will trip by reverse power relay. Due to the presents of Reverse Power relay, it will not allow the Generator to run as an induction generator and will trip the Generator breaker, thus it protect the generator from further severe fault. Again, if it not trips by these all protections, alternator will work as induction generator due to the residual magnetism in the field core when it is running in parallel and it will give the over load to another generator as a result, it will trip entire system. Also, as an alternator typically isn't designed to operate as an induction machine, the windings on these machines will heat up and damage. Therefore, need to make sure the reliability of protection relays to avoid such faults.
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / atul
if excitation fails let d case of hydro generator the prime
mover is turbine. since turbine ic moving and is coupled
with generator shaft and no flux to control its speed it
will go out of path or speed will increase beyond
synchronism
| Is This Answer Correct ? | 8 Yes | 6 No |
Answer / ramlakhan y adav (ballia)
when the excitation is removed then the alternator work as a
asynchronous motor will draw the power from reverse supply.
| Is This Answer Correct ? | 7 Yes | 5 No |
Answer / manjeet
duction generator as underexcitation .
but there is under excitation limit which should slip is
negative
and reverse power flows which will be taken care by
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / raj
Every one is right but one more thing will happen that is
Alternator will work like motor and will draw power from
other source ( with that it synchronised )known as reverse
power and further RPR will trip the Alternator breaker.
(Approx continuous rating for reverse/negative power is 10%)
| Is This Answer Correct ? | 7 Yes | 14 No |
Answer / vijin
if the excitation fails the motor will simply stops,because
it loses the magnetic locking capability by the removal of
dc supply. the motor has no field suplly to generate
necessary emf while running by virtue of the inertia.
| Is This Answer Correct ? | 3 Yes | 14 No |
why inuctive drop is not consider in DC MOTOR
why capacitor bank shorted by resistance ( 3 terminal )
How much water ( Kilo Liters) a submercible pump of 35 HP can lift from Borewell of 6" and 900 feet dip.
HOW TO IDENTIFY THE RELAYS WHICH APPLICATION IN WHICH RELAY USING?
if we supply to secondary winding how transformer work?
We have a bank capacitor rating of 60 KVAR for a overall load of 160 KVA and we have connected three loads of 50KVA each. We would like to auto matically correct PF using APFC. How do we design it?
defination of reactor
what is KA rating and how can we choose switchgears on applications
what is a switchgear. what is its work & where it is used?
how can alculate the apfc panel rating?
How to dimensioning SDCCH, LAPD and CS7 signaling on GSM?
Can neutral line also be use as a earthting for distribution transformer, or we need separate earthing pit forh the transformer?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)